Hi guys having a hard time thinking about weather I should put a 3pole isolator or 3+N on a mains three phase board. It’s at the origin of the system. It’s a TNCS system and I put a 3+N pole isolator for the main switch on the DB, but I’ve had a friend say he puts just a 3 pole. I don’t think there will be much switchgear, if any. Any advice would be greatly appreciated thanks
 
For a TN three phase earthing system in a non domestic environment it isn't necessary to isolate the neutral but there must be a provision to disconnect it (the neutral bar will have a disconnect link). You have done nothing wrong using a four pole isolator but it isn't necessary assuming this is not domestic.
 
For a TN three phase earthing system in a non domestic environment it isn't necessary to isolate the neutral but there must be a provision to disconnect it (the neutral bar will have a disconnect link). You have done nothing wrong using a four pole isolator but it isn't necessary assuming this is not domestic.
 
Hi thanks for the reply, I really appreciate it.

So it’s a odd one, the meter company I believe have put it as a domestic property, I think at first wanted to do commercial but I’m not sure what they settled as, however it’s a chunk of land. The supply has been split with Henley blocks supplying x2 houses 1 phase for each house and then 3 phases for this DB. Which is supplying the rest of the land rather than the houses.
 
If it isn't actually part of a dwelling four pole would not have been required but it really doesn't matter you have it is not wrong to have done so.
 
If it isn't actually part of a dwelling four pole would not have been required but it really doesn't matter you have it is not wrong to have done so.
Ok , thank you very much brother. So not it’s not apart of the dwelling as the houses are being fed from Henley blocks rather than the board so no, thanks a lot!
If it isn't actually part of a dwelling four pole would not have been required but it really doesn't matter you have it is not wrong to have done so.
 
In my opinion a triple pole isolator is safer in a TN installation than a four pole. If the neutral fails to make early and break late you'll know all about what I mean. I'd much, much prefer a bolted neutral.
 
In my opinion a triple pole isolator is safer in a TN installation than a four pole. If the neutral fails to make early and break late you'll know all about what I mean. I'd much, much prefer a bolted neutral.
Ok, interesting I appreciate your reply! But what I’ve done is t wrong?
 