Is such a system (230 volt L-L) legal under BS7671 or IEC 60364? Do I need double pole switches for light fittings?
 
Is such a system (230 volt L-L) legal under BS7671 or IEC 60364? Do I need double pole switches for light fittings?
When you say 'system' is the building supply 2 phases as you describe without a neutral or is this just a final circuit.

Either way the answer is yes in most places on the planet (including Derbyshire....wherever it may be), you'd need every point of consumption including light fittings to be supplied by a double pole switch.

I think England is in Derbyshire and Derbyshire is part of the UK, but I might be wrong :).
 
Last edited by a moderator:
Since 133V isn't a normal supply voltage, SP loads would all have to be connected L-L and for practical purposes it would be used as a delta supply. Whilst delta power is common for certain applications, e.g. shipboard, it can make things a lot harder. All switching and OCP must be DP, so you can't use 13A plugs for example.

Illegal - no, but not terribly useful for most applications and a general purpose electrical installation fed that way might be considered unfit for purpose.
 
Since 133V isn't a normal supply voltage, SP loads would all have to be connected L-L and for practical purposes it would be used as a delta supply. Whilst delta power is common for certain applications, e.g. shipboard, it can make things a lot harder. All switching and OCP must be DP, so you can't use 13A plugs for example.

All loads are indeed connected L-L with 2 pole MCBs used on all circuits.

The switching I am unsure about. Would lights still need DP switching?

Illegal - no, but not terribly useful for most applications and a general purpose electrical installation fed that way might be considered unfit for purpose.

Sounds like a lot of draw backs. Is switching on of them?
 