Is such a system (230 volt L-L) legal under BS7671 or IEC 60364? Do I need double pole switches for light fittings?
No definately illegal. 5 years, no parole.Is such a system (230 volt L-L) legal under BS7671 or IEC 60364? Do I need double pole switches for light fittings?
No definately illegal. 5 years, no parole.
Think the measurement may have been taken between taking two lines of cocaine lolAm I missing something? Where or how are you measuring 230v between two lines?
Am I missing something? Where or how are you measuring 230v between two lines?
Hang about... Do you live in some weird part of the world?
Probably Derbyshire.Hang about... Do you live in some weird part of the world?
When you say 'system' is the building supply 2 phases as you describe without a neutral or is this just a final circuit.Is such a system (230 volt L-L) legal under BS7671 or IEC 60364? Do I need double pole switches for light fittings?
Cape Town.Where do you live?
Since 133V isn't a normal supply voltage, SP loads would all have to be connected L-L and for practical purposes it would be used as a delta supply. Whilst delta power is common for certain applications, e.g. shipboard, it can make things a lot harder. All switching and OCP must be DP, so you can't use 13A plugs for example.
Illegal - no, but not terribly useful for most applications and a general purpose electrical installation fed that way might be considered unfit for purpose.