L

lewlec

Hi all

just wondering if anyone knows if it would be possible to feed two single phase supplies through a 4 pole mccb?

thanks
gary
 
Can you explain the layout? Won't the main MCB/isolator fulfill any requirement for single isolation point?
 
What are your plans for these two single phase supplies that require a single point of isolation?
As above 2 DP's, and if absolutely necessary to have single point isolation, contactors?
 
Ok

i have a new supply installed which is 2 x single phase 100amp and is located remotely from the installation. Now I have a 4 core swa with separate cpc which is run from the cut out position to the installation position. I was wanting 1 point of isolation for the whole install also providing protection for the sub main. Hope this makes sense.

Gary
 
The problem will be if you use 1[SUP]st[/SUP] & 2[SUP]nd[/SUP] Ph for one of the circuits and the 3[SUP]rd[/SUP] Ph & N for the other. Only the 2[SUP]nd[/SUP] circuit will have early make late break for the neutral.

I think you can get a bridging piece for the switch dollies to link two 2 pole Telemecanique MCB’s together.
 
Sorry if I'm a bit slow of the mark tonight, so there's 2 phases and a single neutral at the cutout? This isn't 180 degree split phase is it?
 
Thanks tony

Didnt think it was that simple.
will have a look at the telemecanique kit

regards
gary
 
Sorry if I'm a bit slow of the mark tonight, so there's 2 phases and a single neutral at the cutout? This isn't 180 degree split phase is it?

Hi marvo

no it's purely 2 x single phase supplies, wasn't involved with the supply application. Would have gone for split myself.
 
Gary,

You'd be as well phoning them, if I remember right there's a little inter-trip unit that goes between the two MCB's. It's years since I specified them, we used them in control panels.
 
Thanks for that, I am still waiting to hear from dorman smith with their final thoughts as the guys in tech were looking into it.
 
Let me know what they come up with.

We used the Telemecanique intertrip units and toggle links on vibrating feeder panels.
A fault on ether the mains or control tripped the other. The only trouble, which tripped first?
 
Hi

well to say the least that dorman smith tech is pants! Still waiting for a reply after several phone calls.
any way ended up going for a 4 pole switch fuse but with 2 fuses replaced with copper links, made by a company called switchgear systems also hager offered the the same set up.

thanks for your replies
regards
gary
 