We are looking for a distribution board to provide 3 * 160A three-phase feeds, but they are basically redundant supply path options so max total is 160A as well. I had been looking at using a Hager MCCB panel (as we generally have been using their MCB DBs) but many of them are limited to 125A...
Hi everyone,
Happy Friday!
Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve looked in the BBB but to no avail on the Max Zs tables. I’ve also looked on our Cert software as they have a Max Zs app but the MCCB category doesn’t...
Hi everyone,
Happy Friday!
Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve looked in the BBB but to no avail on the Max Zs tables. I’ve also looked on our Cert software as they have a Max Zs app but the MCCB category doesn’t...
Hi all,
In general do you size the cable to the MCCB full trip setting rather than the adjustable setting for the load being supplied. In some cases upsizing the cable can be costly even from 320/400. One of the site engineers is adamant that it should be sized for full trip setting.
I'm not...
Hi All,
We have a Merlin Gerin Compact NS100N Single Phase MCCB
I've been asked to find its Max ZS Values and to be honest I cant find anything!
This is an from an old MCCB board we are re testing. I put it in google and cant seem to find anything, I know Schneider bought this brand out. But...
Hello All.
New here and will be flooding with terrible questions for my own knowledge. Just trying to learn so some questions like this maybe very simple and I'm just daft
1) On site we have a Aux Transformer,
From the LV side of the transformer we have an MCCB Board with a few circuits.
Now on...
Hi guys. Looking for some advice.
I’ve had some building work done.
1. Outhouse. The wiring internally was changed but the wiring from the house to the outhouse is the same. All electrics working okay in there.
2. Conservatory built. Wiring is in however it is not connected up yet so no...
Hi I have a client with a 1000a merlin mccb as their incoming PD from their private transformer.
Previous maintenance spark has claimed its faulty and trips under no load, so they’re leaving the compressors running 24/7, I find this odd but don’t want to mess around too much as if something...
I am are looking to purchase used and surplus 3 Phase MCCBs and single Phase high amperage MCCBs.
All brands considered as long as the MCCBs are in full working order.
If you have any that fit that description that you would like sell, please drop me a DM.
Thanks
Hi all
We are doing wiring to 6 flats.DNO will provide 200 amps service head on ground floor.All Swas for flat submains come to the intake area on ground floor.
What is the best option for termibating those SWAs into individual switch fuses after Ryefield board or can i use MCCB panel.Do the...
Hager 100A MCCB new type (brand new) is tripping when attempting to switch on - new installation. Circuit is feeding a SWA to a DB - No Load on DB and cables of SWA meggering out ok . Thinking the MCCB may be faulty - anyone had probs with these?
Hi
2 questions really,
im doing a periodic on an old residential home, one of the mccb,s (an old dorman smith single phase 32a) has a small dial bit with 100%/70% on it. what is this?
also i have a em lighting supply leaving the db going to an isolator then on to a big battery(more like 2 LARGE...
Does anyone know of a suitable alternative to a Proteus MCCB, as they seem to be difficult to get hold off, and alot more expensive then a different make, I'm after a 63amp if anyone has got any ideas.
High looking for a bit of advice might be picking this up incorrect.
A main supply panel board with an 800a and 400a mccb feeding a factory an office block respectively.
Tested Ze 0.07 ohms
Production Building Zs 0.04 ohms
Office Block Zs 0.07 ohms
Length of runs from panel board to both...
horticultral lighting circuit - 14 x t/p 16A mcb's each mcb has 6 x 600w 400v son lights, fed from a contactor which is fed by a 160A merlin gerin mccb. across the contactor measures L1 - 130A L2 - 133A L3 - 132A but after 6hrs the 160A trips. any ideas ? there is another 2 identical systems...
Have been looking at a situation where a 400 amp MCCB is feeding a ups. There is a mains supply to a genny changeover switch, along with the genny supply, and the MCCB is between the genny switch and the UPS.
Yes its a big bu##er.
Any ways there was a momentary power fluctuation which threw...
Hi peeps,
I need to out what rating an MCCB is, but cannot seem to find the relevant info on it.
It is an ABB sace, which can be cranked down, and has 5 settings on it. Any advice please will be much appreciated.
Anybody like to take a guess on how much I've been quoted to install a new 125a mccb to an existing panel board (spare cubicle available- work carried out 12am - 6am )