A question regarding the use of a mccb as a 3 phase main isolation switch to a DB.
Is it a necessity?
Current set up is I have a 3 phase 70mm supply feeding a DB.
The origin of this supply is unknown, hence I’m getting northern power out to investigate as the main cut out earthing arrangement and metering is unknown
As I do not know the primary OCPD protecting the 70mm swa and lets assume for the minute that they are adequately protected via bs 1361 or bs 88 fuses, is the mccb totally necessary protecting the DB final circuits?
The existing one is broken and does not isolate the DB.
Spoken to Hager and the range is now obsolete and can’t be retro fitted.
It’s a 250 amp mccb with its In set to 200 amp minimum setting so it’s rated to high for the 70mm swa anyway.
Comments welcome:mtongue::)
 
The current mccb is too large for the 70mm swa anyway, the Ir setting is set at its 0.8 minimum setting giving it an In of 200 amps which I have the 70 mm swa at a ccc of 128 amps reference method D and a correction factor of 0.9 which I already have applied to raise the ambient temperature to 30 degrees inline with section 433 where overload protection is required.
The whole job and trying to salvage circuits for the refurbishment is a pile of s#ite and it’s only 12 years old.
The ventilation system has been installed with soil stack pipe with no back draft excluders for the inline fan venting individual rooms
 
Last edited:
It maybe that the 70 mm swa is the DNO’s cable and the mccb is the device used for protection of the swa against over current
God knows what has happened to the metering tho
 
Is there a way currently of isolating the whole installation?
No
It’s a big issue In itself
As it’s stands all I’m doing at the moment is carrying out an eicr however we will be doing the alterations to the electrical installation during the refurbishment works so it will need addressing
 
Have you had a walk around for any remote brick buildings where the intake could be maybe hidden in bushes.
 
Have you had a walk around for any remote brick buildings where the intake could be maybe hidden in bushes.
I’ve found the supply.
The DNO have been out and their LV supply goes to a meter room housed in another building about 200 meters away from the building im working in.
The 70mm is connected to an old handle bar isolator (looks ancient and if isolated may not reconnect)from which an swa from the DNO’s metering cut out feeds.
Worryingly tho I’ve a 25mm cpc entering the building but it’s a 16mm that connects to the remote isolator at the supply end.
The maintenance guy who looks after the building where the metering is kept informed me that originally the sub mains that was installed back in 2006 was too small so the contractor had to upgrade the cable, all sounds a bit comical.
I need the DNO to tell me the earthing arrangement as I need to assess the possibility that the 16mm/25mm is inadequate for the protective bonding requirements to the building.
There’s no pme label at their end so I’m hopeful that it’s TN-S as the possibility of making the building TT is a no go really.
The LV cable looks like PILC but I’d need to confirm
 

Reply to Mccb used as main switch isolator in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I've been carrying out quite a few domestic extension first fixes recently which involves providing a power supply installed from the properties...
Replies
7
Views
2K
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock