That cant be right, the RCD "starts" to trip at 30mA but it depend what bit of the sinewave its at, in 300ms it could be peak voltage and current.Maybe 1/10 slower but at a vastly different fault current!
The RCD trips at 30mA in 0.3s, that fast enough to save most people from a fatal shock.
The 40A MCB trips at a current in the hundreds of amps in 0.4s
The 0.4s is to keep touch voltages down, prevent damage to cables from long durations of high current faults and that sort of thing.
If you've ever had a shock from an RCD protected circuit you'll know it hurts just as much as non RCD, it just doesnt last as long.