Discuss 4mm on 32a mcb?? in the Industrial Electricians' Talk area at ElectriciansForums.net
K
KNIPEX
Just a quick question for you lot.
would you put 4mm t+e cable on a 32a mcb.
or would you play it safe and stick it on a 20a mcb.
thanks in advance.
4mm can take 32a dont know the exact pages in on suite guide etc but its ok, also alot of the old houses out there are 4mm radials etc.
Yes no problem at all.
I have on occaion wired 4mm radials in kitchens with 32amp ocpd's, with rest of house divided up into 2.5mm radials with 16 / 20 amp ocpd's.
Wouldn't do it my self but I'm sure someone could say if it's clipped direct with ice round it it would be ok forever. What if the ice melts? your'e signing for the situation as you find it . do how bankrobbers practice and play safe
yep same as easy says, kitchens is where ive mainly used a 4mm radial, id use a 35mm back box as well to ease installation. also on a slight tangent! mk's dbl sockets are actually recommended to be installed in 35mm boxes but more often than not are done in 25mm's boxes's
4mm clipped direct has a current rating of 37 amps, all other installation methods drop that rating down below 32 amps.
Ib<In<Iz ..... ?
why wouldnt you do it? it is a perfectly acceptable design solution, and the regs (both 16 and 17th) expressly say you can do it.
i have just put a 4mm radial into a kitchen - what you you say if you found that on a PIR then:rolleyes:
Sure it all depends on the lenght of the cable. it would be ok for a short run. you should work out your volt drop on the cable before anything.
well of course, but whats that got to do with 4mm on a 32A MCB? dont you (we) do that with any cable we design and install?
the regs tell us we can serve an area of 75 metres squared with 4 mm on 32A MCB.
I have done a number of 4mm radials recently, and shall continue to do so:rolleyes:
Reply to 4mm on 32a mcb?? in the Industrial Electricians' Talk area at ElectriciansForums.net
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Have a 63A RCD 5 Way box, with a 45A MCB, feds by 16mm2 tails, this in then feeding into a isolator via 10mm2 T&E, that then supplies the feed to...
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...