yes you're right about the 2.5mm2 only being rated at less than the 32A MCB.
But the 32A MCB is protecting the whole circuit, not JUST the piece of cable (the 'spur') to a double gang socket. The double gang socket is limited to two plug tops, each could contain a 13A fuse. 13+13 = 26. Are you seeing a way out here ....
So if you spurred off the spur, again in 2.5mm2, well then you're asking for (theoretical) trouble, as now you have 2 x 26A potentially going through the 1st, original bit of 2.5mm2 cable. Which would trip the 32A MCB sooner or later, but a bit less and maybe it wouldn't, and then you'd have a cable with a lower current carrying capacity than the current its carrying! Not good. Thats why that's not allowed.
The reason 4mm2 is ok to do this with is it will take 32A and a bit more quite happily, and the 32A MCB will trip before the cable is troubled by excessive load. Assuming the installation methods, ambient temperature, and so on are all acceptable of course.