Found an old property which has 4mm radials on a BS3036 30A, now given the insulation is 100mm, cable are clipped to joist in this bungalow. Does this now need to be on a BS60898 B20? I am carrying out work on the circuit and extending it in 4mm, therefore I have recommended the consumer unit to be changed, to include RCD protection. If it does have to be reduced to 20A, that will reduce the supply. Cheers chaps
 
when you say old property, it might be 7/029, not 4mm. , in which case reducing the OCPD to 20A would be a good plan. first thing is to calculate the load on the circuits and fit a OCPD as low a rating as Iz>In>Ib. most household socket circuits, with the exception of the kitchen, willnever draw more than 10 - 15A.
 
If the insulation is in the loft / attic and is accessable , i'd try and move it away from the cables rather than derate all the socket circuits - 30A to 20A is a big drop , and a kitchen circuit may not run on only 20A.
 
agree with biff. move the crap off the cables.
 
well....theres much exitement about how much is needed to serve points within the home (kitchens excepted)....20A radials=fine in truth it will never see it anyway....
kitchens...give it more on its own....
 