Hi all. I'm after opinions on a proposed modification to a circuit. Would it in theory be permit table to spur from an existing socket point on a ring final in 4mm to service three sockets, in order to remove the need for an fcu? (as it will be a spur of a spur)

My reasoning is that the 4mm is adequately rated to the 32a mcb of the circuit which would remove the need for an fcu? I have tried to extend the ring but I cannot access the cable sat the correct socket so I have to use the only point available to me. There is no space for an fcu where I intend to run the new points (t.v and sky box)

I could also de-rate the circuit and split into two radials but it would be nice to keep the 32amcb. Although not standard, I can't see why it be unsafe ?
Ps...few spelling errors caused by auto fill on my iPad
 
Extend the ring from the accessible socket.
Crimp joint the return leg of the new sockets to the cable at the original socket.
 
reading between the lines, i think OP is connecting into an existing spurred socket, this is fed with a single 2.5mm, so bad idea.
 
The main argument against spurring off a socket that is on the ring in the manner described is the potential for overloading one point of the ring. If you had 3x skt outlets connected in 4mm to a socket on the ring then that point on the ring could be subject to overloading. If the sockets are for AV equipment then not a problem now, but who's to stop folk plugging in numerous arc welders in the future? ;)

I can't understand why you can't just extend the ring as suggested, it is the 'proper' way to add new sockets to a ring!!!
 
never mind all that malarky. who's changed my bloody avatar???????
 
Extend the ring. You'd have "fun" trying to terminate two 2.5's and the 4.0 securely in a socket terminal anyway ;)
 