So why the disagree? The bonding was after the isolation valve where it entered the flat in this case and when I showed him our regs book he didn't take it any further, just pointing out that their regs just stated within 600 of the meter.@anthonybragg if they want a bond at the gas meter then they better put one there themselves
Its up to us to follow BS7671 and it says within 600mm of entering the building and before any Tees or branches. Obviously this isn’t viable all of the time and common sense should prevail but I certainly won’t be changing the way I bond Gas pipes until BS7671 changes