Hi guys
How many amps will a 2.5 flexible cable carry this has been used for a 6.5kw hob
 
Off the top of my head 24 amps, if you go on google you can download a table with the ratings for flexes. these are dependant on length of run,ambient temp etc.
 
Last edited by a moderator:
With reference method C it's 27A so it will have to be 25Amcb

6500W @ 240V - 27.08A
5980W @ 230V - 26A

If you can apply diversity then it will be alright.
 