M michael_brooke Dec 12, 2012 #1 Hi guys How many amps will a 2.5 flexible cable carry this has been used for a 6.5kw hob
G Guest111 Dec 12, 2012 #2 Off the top of my head 24 amps, if you go on google you can download a table with the ratings for flexes. these are dependant on length of run,ambient temp etc. Last edited by a moderator: Dec 12, 2012
Off the top of my head 24 amps, if you go on google you can download a table with the ratings for flexes. these are dependant on length of run,ambient temp etc.
G Geoffsd Dec 12, 2012 #3 With reference method C it's 27A so it will have to be 25Amcb 6500W @ 240V - 27.08A 5980W @ 230V - 26A If you can apply diversity then it will be alright.
With reference method C it's 27A so it will have to be 25Amcb 6500W @ 240V - 27.08A 5980W @ 230V - 26A If you can apply diversity then it will be alright.