Looking for some advice regarding some connections on a heating contactor.

I picked up some readings using a thermal camera which I thought were a tad high. I remade the crimps as these were the "hot spots" however this has had no effect on the temperature.

The current draw is approximately 42 amps as its a radiant heating circuit.

Are these temperatures normal for this scenario? I haven't done a great deal of thermal imaging but when I do I set the camera to flag temperatures above 60 degrees.

See the attached image below:
View attachment 85690
Just out of curiosity have you put an amp meter on it to see what kind of load it’s pulling.
 
Well if you thought the last one was bad, here is an image I took earlier this week. I used the lava pallette and set an isotherm for 70 degrees. Therefore everything showing as "lava" is potentially 70 degrees and higher.

Image taken using the Cat S62 pro.

View attachment 86924
Yeah...once you see temperatures above 65C in a CU or DB, for me it would be time to start investigating. I agree with PC1966, you don't really need a thermal camera above that kind of temperature, you can usually smell that there's a problem when you open the door. I'd assume the problem in the photo was either marginal overload or undersized wiring....or maybe a bit of both.
 
6mm singles enclosed in conduit/trunking is only rated at 41 amps, at that current it would be at 70C, i would be looking at a bigger cable , 10mm will take 57 amps in similar conditions
 
It's not in conduit or trunking, the images clearly show the heat eminates from the connections otherwise the full length of the cable would be overheating, this is not a ccc issue, its either poor quality contactors or cheap terminations.
 