Engineer54
If you use the heat shrink boots suggested by E54 with an external heat shrink sleeve it’s going to be as waterproof as you’ll ever get. The only weak point is where the gland meets the enclosure, if it’s misaligned you can distort the enclosure base plate. This is a point I would disagree with E54. a hefty cable glanded laid flat and then offered up will stress the cable and gland plate.
I first used HS boots on PILC cables as an apprentice, not adhesive lined, they used a hot melt tape. They were supplied with CMP lead lined glands. Brilliant things to work with, heat them up and the lining melted on to the lead sheath. I’d say probably better than a traditional plumbed termination.
RoB2 asked about them recently, no longer available!
Think your getting confused here, ''Boots'' cover and protect connections (normally MV/HV), ''Breakouts'' seal the ends/crotch of the cable after exposing the cores.
This very much depends on the location and how much room you have to work in. If your working out of a decent concrete cable trench under the switchboards, there shouldn't be any problem as far as not stressing the cable. More stress is put on the cable, when we've had to turn the cable for the cores to roughly line up with the terminations in the switch boards. It's also desirable to provide a cable support for heavy cables entering switchboards , panels and the like. Either way glanding off before or after the Top Hat gland has been fitted to the panel, it's a dam sight easier all round than glanding off with a typical SWA brass gland!!
Using glue lined crotch breakouts, with glue lined heat shrink tube, over the cable and gland (any gland type) will as Tony suggested make it about as waterproof as your ever going to get. We use this method all the time on all our external SWA cables...