daveb1

Hi

Half due to me slightly over sizing a cable and the terminals of the MCB being far to small, looks like i need to join 70mm and 35mm conductors together, its underneath a cooking suite in a large commercial kitchen, there will not be a great deal of space to work.
i would like to use a straight through crimp then heat shrink BUT is there some kind of reducer i can use?

Would bolting lug crimps together be a complete lash up?

Any constructive help would be appreciated

Thanks Dave
 
Hi

Half due to me slightly over sizing a cable and the terminals of the MCB being far to small, looks like i need to join 70mm and 35mm conductors together, its underneath a cooking suite in a large commercial kitchen, there will not be a great deal of space to work.
i would like to use a straight through crimp then heat shrink BUT is there some kind of reducer i can use?

Would bolting lug crimps together be a complete lash up?

Any constructive help would be appreciated

Thanks Dave


Copper Pin Terminals - SWA
Copper Pin Terminals - SWA
Copper Pin Terminals. Un-insulated Solid Copper Pin. Un-insulated Reducing Pin ... Site Map · About Us · Company History · Legal · Terms and Conditions.

have a look at these, don't know if they will be any good in your situation for the terminals.
 
Last edited by a moderator:
its a 4 core swa 70mm and the MCB i thought the only option would be connect to 35mm to fit into MCB terminals
 
Thanks guys due to the restricted space to terminate above the mcb i think the SWA mechanical joints look like there perfect job
 