J
Jordanh1992
Hey guys,
A 16mm2, two core armoured, 70 degrees PVC insulated cable (copper conductors), is clipped direct to a surface, and forms the two wire radial distributor shown in the diagram below. The distributor is fed at end A at 230 volts and the cable lengths are as follows:
A to B - 45m
B to C - 35m
C to D - 20m
A. Find the current in each section of the diagram.
B. Use IET Wiring Regulations to calculate the overall voltage drop.
A------B------C------D
20A. 10A. 15A
Firstly it asks me to find the current in each section of the diagram, surely that has already been done for me already(20A, 10A, 15A)??
Also to work out the voltage drop...
16mm2 cable - (mV/A/m) = 2.8 table 4D4B?
Ib - 20A + 10A + 15A = Ib 45A
L - 45m + 35m + 20m = 100m
So... 2.8 x 45 x 100
1000. =12.6?
But surely that's unacceptable because the voltage drop is over 11.5 volts, so 16mm2 cable can not be used? Am I missing something or doing this completely wrong lol, help would be much appreciated..
Many thanks!
A has not been done for you, the question asks for the current flowing in each section. How can the final section have more flowing in it than the middle
Joran,
Trev is right.
Think about what they are asking!
C&G are not known for there clear questions.
can u tell me 2 methods of calculating the volt drop trev?
Did my 2395 tonight, there are two methods to determine voltage drop that is 1.measurement at Origen then at load. 2nd is calculation: v= I x R ( 35 x 0.34 = 11.9 V.) then say 5 % at 230v ( 0.05 x 230 = 11.5 v) this circuit and load at 5% is unacceptable .
i found 2395 intense, hope tomorrows 2394 is less intense.
lester
45m. 35m. 20m.
A-------B------C------D
20A. 10A. 15A
This is the diagram, if you was wondering what it looked like...
I need to find the current in sections
A-B
B-C
C-D
I understand how to work out the voltage drop, just not the first section
I don't see how you're struggling with this Jordan but given that you have the amount of current flowing in each section what do you think the answer is in A - B
For qu A...
A-B carries 45A, B-C carries 25A and C-D carries 15A?
Appreciate your help,
If this is correct, what formula have you used to find the answers..
maybe I'm over thinking this and missing something simple!
im not looking for the answer on a plate for me just abit of guidance.
thanks
thanks
You are over thinking it and it's not a formula mate. 1+2+3 that's all it is.
- - - Updated - - -
I'd have made you work for the answer but others are kinder :)