A 16mm2, two core armoured, 70 degrees PVC insulated cable (copper conductors), is clipped direct to a surface, and forms the two wire radial distributor shown in the diagram below. The distributor is fed at end A at 230 volts and the cable lengths are as follows:
A to B - 45m
B to C - 35m
C to D - 20m
A. Find the current in each section of the diagram.
B. Use IET Wiring Regulations to calculate the overall voltage drop.
A------B------C------D
20A. 10A. 15A
Firstly it asks me to find the current in each section of the diagram, surely that has already been done for me already(20A, 10A, 15A)??
Also to work out the voltage drop...
16mm2 cable - (mV/A/m) = 2.8 table 4D4B?
Ib - 20A + 10A + 15A = Ib 45A
L - 45m + 35m + 20m = 100m
So... 2.8 x 45 x 100
---------------
1000. =12.6?
But surely that's unacceptable because the voltage drop is over 11.5 volts, so 16mm2 cable can not be used? Am I missing something or doing this completely wrong lol, help would be much appreciated..
Many thanks!
A 16mm2, two core armoured, 70 degrees PVC insulated cable (copper conductors), is clipped direct to a surface, and forms the two wire radial distributor shown in the diagram below. The distributor is fed at end A at 230 volts and the cable lengths are as follows:
A to B - 45m
B to C - 35m
C to D - 20m
A. Find the current in each section of the diagram.
B. Use IET Wiring Regulations to calculate the overall voltage drop.
A------B------C------D
20A. 10A. 15A
Firstly it asks me to find the current in each section of the diagram, surely that has already been done for me already(20A, 10A, 15A)??
Also to work out the voltage drop...
16mm2 cable - (mV/A/m) = 2.8 table 4D4B?
Ib - 20A + 10A + 15A = Ib 45A
L - 45m + 35m + 20m = 100m
So... 2.8 x 45 x 100
---------------
1000. =12.6?
But surely that's unacceptable because the voltage drop is over 11.5 volts, so 16mm2 cable can not be used? Am I missing something or doing this completely wrong lol, help would be much appreciated..
Many thanks!