Doesn't matter I've worked it out . Thanks for your help. 1 - 20 + 10 + 15. 2 - 10 + 15. 3 - 15?
 
Right what I was meaning is...for the current flowing in A-B you add up all three figures because it's one section of cable serving 3 points. For the second section you deduct the bit that isn't flowing in that bit IE the bit A-B. For the third bit you deduct the bit that isn't flowing in that bit IE B-C
 
Also to work out the voltage drop...

16mm2 cable - (mV/A/m) = 2.8 table 4D4B?
Ib - 20A + 10A + 15A = Ib 45A
L - 45m + 35m + 20m = 100m

So... 2.8 x 45 x 100
---------------
1000. =12.6?

But surely that's unacceptable because the voltage drop is over 11.5 volts, so 16mm2 cable can not be used? Am I missing something or doing this completely wrong lol, help would be much appreciated..

Many thanks guys and apologise for being a dumbass haha.
 

OFFICIAL SPONSORS

Back
Top