John Adams
DIY
Currently: a detached garage used occasionally as a woodshop with a range of machinery. Only one user. Garage is 25m from CU. Currently supplied with one double socket which is a spur from the ring final. Lighting (3A max) comes off this too. Draw from this source <18A.
CU has a old unused cooker radial with a 32A Type B MCB. 4m of 6mm in plaster from CU, terminating in an accessible junction box.
Requirement: Two new bits of kit brought in from 'proper' workshop have upped power requirements. Do not want a permanent (i.e. expensive) solution, as this shop is only used temporarily. New equipment needs a 16A supply (bandsaw with high startup current but only 1.8kW running) and another item drawing 10A running together. Possibly another item used at the same time, but total new supply required is about 25A.
Possible solution: Change to a 32A type C MCB. Install a 32A 2P+E surface outlet at junction box in house and in garage. From 32A outlet in garage, connect a 16A outlet for saw and a 13A double socket using 4mm T&E in conduit and metal-clad 13A outlet. When power is needed, use a dedicated 32A 25m extension cable (not from Screwfix: a proper waterproof industrial one) to connect the 32A outlet from the cooker radial to the 32A outlet (used as, essentially, an 'inlet') in the garage.
Would this work, and is it fully safe? I do not want to install a permanent new supply, but equally I'd like something a bit more robust than trailing extension leads all over the place, and cutting the 16A plug off the bandsaw and replacing it with a 13A one (which is quite common, it seems, and no tripping occurs).
Would be grateful for your not answering if your answer is going to be 'get an electrician'. Thanks.
CU has a old unused cooker radial with a 32A Type B MCB. 4m of 6mm in plaster from CU, terminating in an accessible junction box.
Requirement: Two new bits of kit brought in from 'proper' workshop have upped power requirements. Do not want a permanent (i.e. expensive) solution, as this shop is only used temporarily. New equipment needs a 16A supply (bandsaw with high startup current but only 1.8kW running) and another item drawing 10A running together. Possibly another item used at the same time, but total new supply required is about 25A.
Possible solution: Change to a 32A type C MCB. Install a 32A 2P+E surface outlet at junction box in house and in garage. From 32A outlet in garage, connect a 16A outlet for saw and a 13A double socket using 4mm T&E in conduit and metal-clad 13A outlet. When power is needed, use a dedicated 32A 25m extension cable (not from Screwfix: a proper waterproof industrial one) to connect the 32A outlet from the cooker radial to the 32A outlet (used as, essentially, an 'inlet') in the garage.
Would this work, and is it fully safe? I do not want to install a permanent new supply, but equally I'd like something a bit more robust than trailing extension leads all over the place, and cutting the 16A plug off the bandsaw and replacing it with a 13A one (which is quite common, it seems, and no tripping occurs).
Would be grateful for your not answering if your answer is going to be 'get an electrician'. Thanks.
- TL;DR
- Non-permanent supply to garage repurposing cooker radial using 32/16A outlets and extension lead.