A customer has been quoted 11,000 quid to upgrade to 3 phase a whole load of cable and a pole mounted 11kva are required is 11kva a standard or are they punting us one so to future proof further requests for loads
P
 
I've just been quoted £129,000 to have a 750Kva transformer installed 100 mtrs away from the supply network. This includes the supply, installation & connection of the HV cable, associated protection devices & switch gear and the supply, installation and connection of the transformer, protection devices & switch gear.

The HV supply is 11KV to the proposed transformer
 
the guy from SSE has told me that there is already 46KVA at the property but it is on one phase via the L1 and L2 and 2 cutouts OK I get that, so why add the 11KVA tranny and replace about 200 mtrs OH LV, anyone have any idea whats going on here, is my usual way of conversion letting me down KVA 46 x 1000/230 = 200 Amps which means the 11 KVA =48 amps so why part with 11,000 quid for an extra 48 amps perhaps I am wrong, any thoughts
 
Sounds like confusion here. Overhead supplies are often 11kV (kilovolts), either single-phase or 3-phase. I don't think 11kVA (kilovolt-amperes) is relevant. It sounds like they need to replace the single-phase 11kV overhead line with 3-phase, and replace the single-phase 46kVA transformer with a 3-phase one of suitable size. If the new service is to be 100A, the transformer needs to be at least 3 x 100 x 230 = 69kVA.
 
As always , I am probably wrong but it sounds like you have a 480v splitphase supply at the moment , and 46KVA would give you 2 x 23KVA = 2 x 100a in incomers.
Alot of places out in the sticks used to have it , I have heard it referred to as poor mans 3ph !
They will need the swap out the transformer and add an extra wire in for it to run 3ph to you .

If anyone else wants to use the new infrastructure within a set period they will compensate your client part of the costs for allowing a 3rd party to use what he has paid for to upgrade the line.
 
I may be wrong on the 2 x 23KVA giving you 2 x 100a !?
If it is true splitphase I think you need to factor more in to the equation?
If one of our more learned posters could shed some light , I would be very grateful.
 
Sounds like confusion here. Overhead supplies are often 11kV (kilovolts), either single-phase or 3-phase. I don't think 11kVA (kilovolt-amperes) is relevant. It sounds like they need to replace the single-phase 11kV overhead line with 3-phase, and replace the single-phase 46kVA transformer with a 3-phase one of suitable size. If the new service is to be 100A, the transformer needs to be at least 3 x 100 x 230 = 69kVA.
I get it now I have misread one of the documents I think so I'll re read it
Thank you
 
I may be wrong on the 2 x 23KVA giving you 2 x 100a !?
If it is true splitphase I think you need to factor more in to the equation?

Nope, nothing wrong with that. Consider a transformer with two 230V secondaries rated for 100A. Connecting them in parallel gives you a single-phase 230V supply good for 200A or 46kVA. Connecting them in series gives you a 460V supply good for 100A or 46kVA, but if you earth the centre-tap and call it neutral, you can deliver it as 2x 100A 230V supplies but now with 460V between the lines if desired for high power loads.
 
So is 11KV not overkill for a single customer

It's not a matter of overkill. It sounds like the nearest 3-phase of any sort is 11kV, some distance from the present transformer location. To bring 3-phase to the property, they either have to convert the existing single-phase 11kV line to 3-phase and change the transformer, or put the 3-phase transformer where the 3-phase presently ends, and run the service from there to the property at 230/400V. Depending on distance, that might either be impossible, or might involve massively more copper, so converting the 11kV to 3-phase is likely the most sensible.

11kV line is cheap, that's why it's everywhere. Your 3x 100A supply at 230/400V only takes about 4A from the 11kV line so it can be a very lightweight cable, and two of the three conductors are there already.
 
This is more or less how I envisaged. The red line is the 3-phase 11kV going past the location but the branch to the transformer is only single-phase, so that needs upgrading. Then the transformer gets changed to a 100kVA 3-phase one, and the overhead 230/400V cable from that to your customer, which is also single phase at the moment, needs replacing with 3-phase as well.

Seeing as your premises could be taking over 2/3 of the transformer's rating (69kVA of the 100kVA) it's not as though they are over-speccing it at your cost. Looks fine to me.
 

Reply to A query about KVA and cost in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
759
Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K
Been to a fault finding job and lights where tripping the rcbo. After further investigation we found that it was a blue strapper cable (old...
Replies
17
Views
3K
I have a customer with a farm who has a barn containing a large 3 phase generator which powers various equiptment at that location. A single...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock