This is more or less how I envisaged. The red line is the 3-phase 11kV going past the location but the branch to the transformer is only single-phase, so that needs upgrading. Then the transformer gets changed to a 100kVA 3-phase one, and the overhead 230/400V cable from that to your customer, which is also single phase at the moment, needs replacing with 3-phase as well.
Seeing as your premises could be taking over 2/3 of the transformer's rating (69kVA of the 100kVA) it's not as though they are over-speccing it at your cost. Looks fine to me.