Discuss A technical question regarding the use of AFDDs in the UK Electrical Forum area at ElectriciansForums.net

Pete999

-
Esteemed
Arms
Reaction score
17,092
I seem to remember whilst at the NICEIC film show (oh by the way I believe NAPIT are doing a roadshow as well, lets hope its better than the NICEIC one, see Julys PE for details)
One of the things I remembered from the very limited information given out, was the fact that AFDDS would not be suitable for use on a RFC , explanatios weren't very clear, with no way of asking questions, on to the next topic PDQ.
Does anyone have or know why this is so? would be nice to find out, so if any of you technophobes have any idea, could you post up your thoughts.
 
maybe because the switches on sockets arc a bit when switching under load.
 
According to the Beama guide to AFDDs:
An AFDD will afford the necessary protection to a ring final circuit including to the equipment connected to the ring. It should be noted that a series arc in a leg of a ring final circuit (for example due to a break in the conductor or a loose connection) will not be of a sufficient magnitude to pose a fire hazard as a result of that arcing. In such an occurrence, the arcing will be minimal presenting a high resistance causing the load current to flow through the other leg of the ring final circuit and as such will not be detected by an AFDD.
 
Curtesy of Hager;

Contrary to common belief, AFDD’s do offer protection against arc faults in ring final circuits and to the equipment being fed from this circuit. A series arc fault in one leg however, is unlikely to be at a dangerous level so will not be detected. This is due to current in this instance flowing around the other leg of the ring. A series arc fault will be detected in equipment and in flexible cables connected to the ring final circuit. Parallel arc faults are detected and disconnected in all parts of the ring circuit and on all connected equipment.

Underlined the additional bit to Richards answer.

BEAMA do a guide as well.
 
Last edited:
Thanks to Richard, Tel and Midwest, so I misunderstood the NIC explanation? Or the NIC info was duff? I did wonder at the time "what is the point of using them if you couldn't use them in RFCs. thanks again Lads cleared that little issue up very nicely, no more sleepless nights worrying about it now :tongue::thumbsup::eek::p:confused:
 
Last edited:
Thanks to Richard, Tel and Midwest, so I misunderstood the NIC explanation? Or the NIC info was duff? I did wonder at the time "what is the point of using them if you couldn't use them in RFCs. thanks again Lads cleared that little issue up very nicely, no more sleepless nights worrying about it now :tongue::thumbsup::eek::p:confused:

The NIC information probably wasn't the best. There's been a lot of misconception surrounding them.

I've seen and used them in the US, now I'm not sure if the construction of the units are to the same standards in the European models (can't see why not).

They are far more of a nuisance than anything. The idea behind it makes sense, however they are being introduced before the technology is properly functional.

Can you imagine the amount of ----ed off people there are going to be, half the house trips out everytime the compressor in the fridge switches on for example.

Oh, and there is no way of testing one outside of a laboratory. Do you think each one will be tested before reaching the market?
 
The NIC information probably wasn't the best. There's been a lot of misconception surrounding them.

I've seen and used them in the US, now I'm not sure if the construction of the units are to the same standards in the European models (can't see why not).

They are far more of a nuisance than anything. The idea behind it makes sense, however they are being introduced before the technology is properly functional.

Can you imagine the amount of ****ed off people there are going to be, half the house trips out everytime the compressor in the fridge switches on for example.

Oh, and there is no way of testing one outside of a laboratory. Do you think each one will be tested before reaching the market?
Do Bears s--t in the woods? thanks Rob
 
I can't see any reason for installing any re settable, electro/mechanical operational protective device without a method of test operation. Maybe I need to get a bit more savvy.
 
They have a test button and apparently they test themselves periodically; and if they are not happy, will turn themselves off. Can you imagine the chaos thats gonna cause :)

Still we most not act like Luddites.
 
Courtesy of Hager;
Contrary to common belief

I misunderstood the NIC explanation? Or the NIC info was duff?

The NIC information probably wasn't the best. There's been a lot of misconception surrounding them.
Presumably NICEIC are pandering to common beliefs and misconceptions rather than technically detailed information, who would have thought it!:):)
 
Presumably NICEIC are pandering to common beliefs and misconceptions rather than technically detailed information, who would have thought it!:):)

Actually, I got my brief, same as the Hager guidance, from Certsure's Connection magazine, just couldn't find it for the OP, so used Hagers.

Perhaps the 'Faraday Lecture' resulted in Chinese whispers or miscomprehension?
 
Midwests post is about the best summary you will get, mind I gather Hager are buying their AFDD in from another of the big players!

The technology is immature yet and not ready for market.
There are similarities in the devices between the EN & the US standard, but I know that one of the biggest players HQ based in Germany, believes that the US spec is rubbish compared to the EU one.
I will find out more next week when I get an "18th ready" board from one of the OEM's I hope...
 

Reply to A technical question regarding the use of AFDDs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
504
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
First I will pose the question so you don't need to read the rest if you don't want to: What if any are the possibilities that a pretty long RG6...
Replies
11
Views
2K
Hello i've recently just had a re wire done on a three bed semi house, Ive noticed a few things im not 100 percent on ive spoken to the firm that...
Replies
24
Views
5K
I highlighted the condition of an installation several months ago to a client. In short there is a basement which is very wet and the board...
Replies
15
Views
2K
Toneyz
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock