some help with terminal connections top of contactor terminals 1,2. a1 bottom terminals a2 , 2, 4, sorry a little confused.
 
A1 & A2 coil connections. The others aux contacts probably a n/c and a n/o.
Are you sure the other terminals are not 1,2,3,4,
 
hi the job is for a plumber whos asked me to connect a two channel time clock to control the htg and hot water. the problem is there our to separete pumps one each so i was thinking from terminal3 of time clock to the live of the pump live out of pump to a1 on contactor a2 contactor to the boiler, same with the heating . im struggling with terminal 1,2, on the top of contactor and 2,4, on the bottom .
 
post a picture. then we can get an idea. a1 and a2 are the coil on all contactors. check the voltage required. generally, the top terminals are supply, and the bottom the load.
 
Is it a standard domestic central heating system? Don't know why you would need a contactor for that
 
Struggling a bit with your description of things but I don,t think you,re along the right lines. Without better detail it,s hard to advise on it.
But the time clock should be controlling the contactor coil and the aux relays supplying the two pumps.
 
the boiler is a heating unit only there is no valves etc . the boiler connection our l.n.e. only.the trouble i have got is that both pumps go to the live of the bolier so im trying to to stop both pumps working together. i hope this helps
 
Edit...actually you need 2 relays......live return from each room stat will energise the 2 coils and feed each pump ....permanant live to each relay common...then boiler live fed from both relay N/O contacts looped together.
 
Last edited by a moderator:
Have you a wiring diagram of it? By what you're saying is that whichever the time clock is calling for heat or hot water they're both on at the same time ?
 
If there's no stats...(???)...then your clock outputs take the place of stat returns in my description.
 
Just wire it with 2 relays or contactors using the timeclock lives for heat and hot water as the trigger for each, permanent lives in top of each and one pump in the bottom of one and the other one in the other one
 