UK Advice for vending machine

Hi everyone, I need a advice , I’m looking to buy a vending machine, manufactor said the consumption is 3.5kw, peak 5kw for few seconds. They installed a 16amp comando socket. I know when its reached 5kw will need more then 16 amp, or I am wrong? I know the wattage divided by voltage resulting Amp. I request them to install a 32 amp comando socket , machine will run 24 hours. I was wrong? Thank you in advance.
 
It's possible the 5kw is the compressor kicking in.
It's possible the 5kw is the compressor kicking in.
Yes, thank you for your answer, to be honest is a very complicated machine, compressor, grinder, ice maker, when all kick in will spike to 5k for few seconds, but the question is 16amp plug will be enough ? 5000w divided by 220v is 22.72 amp. Machine will run 24h, will not overheat socket? Blow a fuse?
 
A few seconds is a long time for a motor start up it is generally momentary and can be 5 - 8 times the full load current and is not normally considered in calculations although cables can be sized for the momentary volt drop. A few seconds may well trip a circuit breaker depending on it's type and size so you need to establish what actually causes it. It is highly unlikely it will affect the 16A plug and socket but nuisance tripping needs to be addressed.
 
Can you check if this is maybe a 3 phase machine?

You are also dividing 5000 by 220, not 230 volts, but it’s not making much of a difference in Amps
 
A pragmatic answer (setting aside any possible regulatory issues) is that a 16A commando plug/socket should be quite happy dealing with a 3.5kW (~15A) load all day long, including the occasional burst of 20A ish. Also I suspect the 3.5kW could be a maximum figure, not continuous (worth checking). The 'type testing' rules for some appliances require the maximum 'worst case' power consumption to be put on the rating plate and in the spec, which doesn't necessarily represent a lower average when in use.

Of more concern is the adequacy of the installation and rating of protection, as per Westward.

If the manufacturer gives you a genuine UKCA certificate underwritten by a recognised accredited body, and the instructions say 16A, you are entitled to take that as correct!
 
A pragmatic answer (setting aside any possible regulatory issues) is that a 16A commando plug/socket should be quite happy dealing with a 3.5kW (~15A) load all day long, including the occasional burst of 20A ish. Also I suspect the 3.5kW could be a maximum figure, not continuous (worth checking). The 'type testing' rules for some appliances require the maximum 'worst case' power consumption to be put on the rating plate and in the spec, which doesn't necessarily represent a lower average when in use.

Of more concern is the adequacy of the installation and rating of protection, as per Westward.

If the manufacturer gives you a genuine UKCA certificate underwritten by a recognised accredited body, and the instructions say 16A, you are entitled to take that as correct!
A pragmatic answer (setting aside any possible regulatory issues) is that a 16A commando plug/socket should be quite happy dealing with a 3.5kW (~15A) load all day long, including the occasional burst of 20A ish. Also I suspect the 3.5kW could be a maximum figure, not continuous (worth checking). The 'type testing' rules for some appliances require the maximum 'worst case' power consumption to be put on the rating plate and in the spec, which doesn't necessarily represent a lower average when in use.

Of more concern is the adequacy of the installation and rating of protection, as per Westward.

If the manufacturer gives you a genuine UKCA certificate underwritten by a recognised accredited body, and the instructions say 16A, you are entitled to take that as correct!
Thank you for your reply, helps a lot. 👍👍👍
 
A pragmatic answer (setting aside any possible regulatory issues) is that a 16A commando plug/socket should be quite happy dealing with a 3.5kW (~15A) load all day long, including the occasional burst of 20A ish. Also I suspect the 3.5kW could be a maximum figure, not continuous (worth checking). The 'type testing' rules for some appliances require the maximum 'worst case' power consumption to be put on the rating plate and in the spec, which doesn't necessarily represent a lower average when in use.

Of more concern is the adequacy of the installation and rating of protection, as per Westward.

If the manufacturer gives you a genuine UKCA certificate underwritten by a recognised accredited body, and the instructions say 16A, you are entitled to take that as correct!
 

Attachments

  • IMG_5309.jpeg
    IMG_5309.jpeg
    1.9 MB · Views: 51
Which one of those MCBs does the 16A socket?
The middle 32A RCBO is labelled "ice maker switch power" on the outgoing cable. On the basis the OP mentioned 'ice maker' I assume it would be that one, but worth confirming..
On the RCBO's the L and N in and out seem to be the opposite way round to expected, does that matter?

Looks more like an industrial control cabinet than a CU?
 
I saw that but if it is that then 32A is oversized for a 16A socket, it is also a Type A device.
 