This might be a bit of an essay so please bear with me;

We do bits of work at a engineering firm in Manchester and last week we were asked to move a lighting board urgently so they could install a new machine, machine was being installed Monday we got told Friday.

Anyway on moving the board I noticed that the existing board was very warm to touch and the lighting circuits were wired in 1.5mm but all on 16A breakers. Anyway I cracked on and began testing and some of the IR tests were suspiciously low. (Still very acceptable results) & tried reducing the MCB size to 10A to no avail.

I noted it down on the certificate, but nothing was said, since we finished in the early hours. I phoned on the Monday to discuss the work and highlight the fact. They said they would look at it but I never heard anything and was debating what to do at the back of my mind. Yesterday we got another call out to say the heating wasn't working. Again I was greeted by the heating supplies on a 16A breaker but this time fed via 1.0mm, I tried reducing to a 6A and then 10A but again the kept blowing. This time I spoke to one of the Directors who was asking what I meant (he has limited electrical knowledge) Upon further investigation I have also found other sections of the factory where the lights and other circuits are protected by 16/20A and sometimes even 32A but yet fed in 1.5mm and 1mm. Some of the conduits and DB's around the place are warm/hot to touch.

I gave them the spiel about the risk of fire etc and now that I had told them about the issue the worst case scenario could be corporate manslaughter. Anyway they have asked for a written report on my findings but not an EICR.

I'm wondering what you guys would put in the report and advice on how to structure it. This is what i'm planning;

State which circuits I know that the wiring is undersized. (Back it up with a cable calc & the relevant regs)
State the risks of undersized cable.
Recommend for the circuits to be rewired & also an EICR on 100% of the circuits.
Also provide a ball park figure of how much the rectification work will cost & estimated time (down time is important here)

Anybody got anything else to add or advise?

I will post up the finished article here if enough people participate.
 
What you have there sounds fine to me with one change, I wouldn't put a price. There are a couple of ways to sort the wiring/MCB/circuit balance and loads, so offer some solutions and their associated down time estimates, but don't price them. I say this for two reasons, firstly it's a condition report and secondly you don't yet know what work will be required. So if they want a quote then they can ask for one and you will have something more solid to base it on.
 
With most companies:

a/ it's more than £15
b/ it's working now
c/ can we get away with it and do nothing

Answer Yes to any question then forget it.

I'm sorry to say I've sat at my desk srewing up reports about defective wiring. Why should I get my --- chewed off for suggesting spending money when it didn't improve production. I know it needs doing, but nobody will sign the cheque!
Now if I had the production cheque book in front of me. Yeh, we'll have 250 of them, 400 of them and have you got? Could do with some of them.
 
I'm hoping I can convince them to change the existing fittings (400w Mecury) to something more sustainable (T5/LED) and produce a savings calculation which I'm hoping may ease the pain a little bit. However like you say, nobody wants to spend anyway, never mind in the current financial climate!!
 
Whatever you write, keep it factual, not opinion, and keep it honest, and be blunt and to the point. We are into the realms of Health and safety at work and all that comes with it. They need to know how and where they stand from legal point.

Rather than spend an age doing cable calcs and the like, look at the legal standing, and the possible outcomes, and enlighten them to their obligations. I did a full PIR a couple of years ago, and it came about after a totally unrelated accident, the HSE got involved, and when they open up cans of worms, they open them up properly. It cost the company a lot of money to get things back up to scratch, no just electrically, but everything else and they had 30 days to do it in.

Cheers...........Howard

Cheers...........Howard
 
Issue a DANGER notice like this one initially for each circuit that you have come across in you work so far.

I issue these if I see anything that is a C1 or C2 and I don't get a mandate to get on with fixing. I send them to the person ordering the work - I don't charge for them, if they want further information, then I ask for PO coverage for the items that need further investigation.

What I would not do is even THINK about solution (such as LED lighting at this stage).

Once they have the message about the dangers they will come to you and if they don't then you have covered yourself legally I recon.

Doesn't the red printing look great:)
 
Funny thing is I do wave my arms about when I present them

- - - Updated - - -

Funny thing is I do wave my arms about when I present them
 
Its most likely that production has overtaken the original building services infrastructure and rather than periodically upgrade they have just stuck extra loading onto the system, uprated protective devices to cope, added more circuits into busy enclosures etc....Standard manufacturing process of small to medium companies.

IMO and experience, you will need to make it clear that there is danger leaving it as it is and not allowing for future expansion.
Keep any documentation straight forward and list the dangers.
Its not worth the time involved to go into great detail, keep that for later, when you get the refurbishment.

We did an I&T on a factory complex where the trunking was so hot you could fry your bacon and eggs on it ! They were given the schedules with a full report and a price for upgrading. They never got back to us. We read six months later that the factory had burnt down.

So keep it simple so your back is covered......
 