This might be a bit of an essay so please bear with me;
We do bits of work at a engineering firm in Manchester and last week we were asked to move a lighting board urgently so they could install a new machine, machine was being installed Monday we got told Friday.
Anyway on moving the board I noticed that the existing board was very warm to touch and the lighting circuits were wired in 1.5mm but all on 16A breakers. Anyway I cracked on and began testing and some of the IR tests were suspiciously low. (Still very acceptable results) & tried reducing the MCB size to 10A to no avail.
I noted it down on the certificate, but nothing was said, since we finished in the early hours. I phoned on the Monday to discuss the work and highlight the fact. They said they would look at it but I never heard anything and was debating what to do at the back of my mind. Yesterday we got another call out to say the heating wasn't working. Again I was greeted by the heating supplies on a 16A breaker but this time fed via 1.0mm, I tried reducing to a 6A and then 10A but again the kept blowing. This time I spoke to one of the Directors who was asking what I meant (he has limited electrical knowledge) Upon further investigation I have also found other sections of the factory where the lights and other circuits are protected by 16/20A and sometimes even 32A but yet fed in 1.5mm and 1mm. Some of the conduits and DB's around the place are warm/hot to touch.
I gave them the spiel about the risk of fire etc and now that I had told them about the issue the worst case scenario could be corporate manslaughter. Anyway they have asked for a written report on my findings but not an EICR.
I'm wondering what you guys would put in the report and advice on how to structure it. This is what i'm planning;
State which circuits I know that the wiring is undersized. (Back it up with a cable calc & the relevant regs)
State the risks of undersized cable.
Recommend for the circuits to be rewired & also an EICR on 100% of the circuits.
Also provide a ball park figure of how much the rectification work will cost & estimated time (down time is important here)
Anybody got anything else to add or advise?
I will post up the finished article here if enough people participate.
We do bits of work at a engineering firm in Manchester and last week we were asked to move a lighting board urgently so they could install a new machine, machine was being installed Monday we got told Friday.
Anyway on moving the board I noticed that the existing board was very warm to touch and the lighting circuits were wired in 1.5mm but all on 16A breakers. Anyway I cracked on and began testing and some of the IR tests were suspiciously low. (Still very acceptable results) & tried reducing the MCB size to 10A to no avail.
I noted it down on the certificate, but nothing was said, since we finished in the early hours. I phoned on the Monday to discuss the work and highlight the fact. They said they would look at it but I never heard anything and was debating what to do at the back of my mind. Yesterday we got another call out to say the heating wasn't working. Again I was greeted by the heating supplies on a 16A breaker but this time fed via 1.0mm, I tried reducing to a 6A and then 10A but again the kept blowing. This time I spoke to one of the Directors who was asking what I meant (he has limited electrical knowledge) Upon further investigation I have also found other sections of the factory where the lights and other circuits are protected by 16/20A and sometimes even 32A but yet fed in 1.5mm and 1mm. Some of the conduits and DB's around the place are warm/hot to touch.
I gave them the spiel about the risk of fire etc and now that I had told them about the issue the worst case scenario could be corporate manslaughter. Anyway they have asked for a written report on my findings but not an EICR.
I'm wondering what you guys would put in the report and advice on how to structure it. This is what i'm planning;
State which circuits I know that the wiring is undersized. (Back it up with a cable calc & the relevant regs)
State the risks of undersized cable.
Recommend for the circuits to be rewired & also an EICR on 100% of the circuits.
Also provide a ball park figure of how much the rectification work will cost & estimated time (down time is important here)
Anybody got anything else to add or advise?
I will post up the finished article here if enough people participate.