T
Tridentsystems
Morning all. As a qualified spark with part p etc I have gone back on the tools after 20 years of low voltage work on CCTV etc ( please don't hold that against me ! ) my query is how to cover myself for a site visit yesterday. I was asked to quote to replace an old Wylex for a new split load RCD db. During visual inspection and some removal of covers I discovered the ring main is no longer a ring ( disconnection from last socket to fb due to removal of a socket some time in the past. And only the first socket has cpc. Earth had been achieved with conduit in past but various alterations over the years have broken continuity of this. In summary no earth on sockets, 12 sockets on a 30 a rewirable as a radial. And no main bonding anywhere. Obviously I haven't done any work and won't in current state. Advised customer in very plain language the dangers but they have a complete refusal to remedy the situation. I have even advised a second opinion from another spark of their choice but attitude is its been ok for 18 years ! Do I need to cover myself with paperwork sent anywhere ? They refuse to sign anything. Or do I just forget it and wait to. See them on the news ? My worry isn't with stupid adults but the kids in the house. What would anyone suggest to try to change their minds ?