Discuss AM2 assessment in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
Mark.W
Hi peeps,
I recently sat my AM2 and have been told that I did not meet the required standard on 2 sections.
Can someone please explain how to safely isolate the DOL starter. What I did was isolate and lock off the MCb, selected the voltage indicator checked it was working on a proving unit. I then tested L1-L2, L1-L3, L2-L3, L1-E, L2-E and L3-E. There was no N at the motor! I then rechecked the voltage indicator on the proving unit.
I also failed on the installation of lighting circuit, but I'm sure it was fine, it tested out fine and was fully operational at all 3 switches. I took my supply to the light fitting then the PL and SL to the first switch which was connected to the strappers. I linked the commons in the intermediate switch. Not sure what I could have got wrong!
The last thing I failed on was the installation of the swa to the 3ph socket? I terminated the gland either end ran a fly lead from the gland in the DB to MET, and a fly lead to the 3ph socket from the isolator via the earth screw on the isolator cover, all tests were good.
Please can someone she some light on what I could have done wrong?
Many thanks
Do I need to sleeve the strappers?! The AM2 guide on ----------- shows no sleeving?! I just want to know if I can appeal these things?!
Sent from my iPhone using Tapatalk
What's ----------- ? I would suggest looking at 514.3.1, table 51 and 514.3.2
----------- is a website that gives guidance on assessments etc. In particular the AM2.
If you have not installed in accordance with BS7671 I would not think that having taken advice from a third party website not affiliated with the IET or any body associated with the AM2 would be grounds for an appeal.
Makes sense, but if that is all I got wrong and now have to pay £300 for a resit then it seems a bit harsh!
I got told by my assessors that they didn't know how the faults were weighted in terms of points. They just sent off their judgements and it was marked by others. They said they regularly saw surprise fails though.
Heartbreaking really! 8 hours in a booth and having failed on not sleeving strappers! Now I have to do it all over again and pay £300! Gutted to say the least! Surely that can't warrant a fail.
I would have thought not. Not as a lone issue. I feel there must have been other things too. No offence intended though.
yeah table 51 seems pretty clear on it to be honest (and is always gonna supercede an unaffiliated website.. )
you didn't mention asking permission to isolate the DOL circuit? maybe it was assumed as part of the isolation and locking off so forgive me asking, but i've heard it's an easy place to instantly fail the 2394 so thought i'd check :)
Yeah I did ask for permission! Just wondering if it's because I never switched the rotary switch on on the DOL brfore testing at the motor.
No offence taken. There was definitely nothing else wrong with it. Functional testing was fine and I've installed plenty over the years.
The AM2 is in effect one of your final exams before you enter the world as a fully qualified electrician, so it may seem quite harsh, but if you don't know the regulations and how to do the job correctly then you should quite rightly fail it.
As has been suggested earlier, 'spakyfacts' is not the regulations or any sort of recognised best practice guide.
Should the strappers be sleeved? Well it all depends on what colour they are to start with, it's a single phase lighting circuit so the only colours you can identify live conductors with are brown for line and blue for neutral, anything else does not comply with the regulations.
Safe isolation, it sounds like you have isolated the wrong thing, or possibly tested in the wrong place for the means of isolation you have used. If you are asked to isolate a specific piece of equipment then isolate it at its nearest lockable isolator.
Did you ask permission to isolate, fill out any permits required, fit a suitable label and keep the key secure? All things which are easy to overlook.
You haven't mentioned a connection from the gland at the isolator to the earth terminal of the isolator, did you fit this?
Sent from my iPad using Tapatalk
Thanks Davesparks.
I only used ----------- as a guide. I can now see that the strappers need sleeving, not convinced it warrants a fail though.
Safe isolation - I was told we were to replace the motor as it was faulty. I asked for permission to shut down, I isolated the circuit at the Mcb, locked it off and put the key in my pocket. There was a warning label on the padlock. I then took the voltage indicator and tested it on the proving unit. I then tested L1-L2, L1-L3, L2-L3, L1-E, L2-E and L3-E at the motor terminals. There was no N. I then rechecked the proving unit. ( should I have rather isolated at the DOL instead? )
I took a fly lead from the gland to the earth terminal in the isolator and then from there to the socket.
Cheers for your help
Did you not need to test the voltage at the DOL starter?.
By only testing at the motor you haven't proved that the motor may not start up as it is controlled by the starter. The contactor was open so the motor would be dead, but you need to prove the starter isn't going to operate.
Sent from my E5823 using Tapatalk
Hi peeps,
Many thanks
mediate
May be Me or You but you say you linked the commons at the intermediate, not sure what you mean?
I linked the brown conductors at the intermediate switch (in a choc block) and put the strappers into L1 and L2
testing at the motor is an instant fail, removing the terminal box lid should always be done AFTER proving dead
Ah with you now, it's a sickener when you fail an exam, good luck next time
Sat my AM2 a month or so ago at SETA (Southampton), with regards to your lighting circuit its shown on the spec I had that you require a neutral at every location.
If you're saying you didn't sleeve the common at the intermediate this is probably the reason for failing.
I was asked to perform safe isolation on the lighting circuit rather than motor, on the "pre AM2" course I went on they were very specific as to where to measure from - I had to measure at the ceiling rose itself rather than the DB!
One of my lads failed his AM2 first time because he didn't follow the lighting drawing.
Which wanted the feed ran all the way round to switch 3, he just wired it shortest route.....
If you took the feed to the light and the course is still the same I would say that was the main issue.
I agree with others above, I've been informed by my last apprentice that sat the AM2 a couple of weeks ago, spec says neutral required at all switches. Also I assume you had to wire it in T&E/3c&E, therefore sleeving will be required.
My training provider does an AM2 refresh day prior to taking the exam, this kind of input would appear to be invaluable as they will no doubt cover the most common points of failure and give you hints and tips.
Yes we do a refresh course ourselves. Unfortunately we didn't get a heads up about the change. Luckily the two guys who went through without being aware of this read the spec carefully and passed. I can imagine it would be easy to miss something like that under exam conditions. I do always stress reading the spec carefully in case of changes. I'll be informing all my other apprentices.
Sent from my Nexus 5 using Tapatalk
I am to do my AM2 in a couple of months. Does anybody have any good information that can help me prepare for this?
My whole apprenticeship has been spent in new house builds, I have not done any motors, single cores, intermediate switching, swa of such.
My college assessor believes the refresher course before will somehow have me prepared, I feel scepticle about the whole idea that 1 day course can give me all the stuff ill need to pass.
Any information would be greatful.
I haven't a clue what you're talking about matey I'm not an electrician. I just clocked that they were added by one of the lads and you'd asked about whatever it is and I remembered.
However hang in there, as some of the lads might be able to help you out.
I wouldn't worry too much about the s plan as you are given a complete schematic on how to connect it. What I would say is try and leave enough time to get it done.
Yeah I'm determined to get everything out of the way quickly as possible, as these heating systems always seem to give me the jitters. Overall I've never been one for anything involving exam conditions!
Reply to AM2 assessment in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
attempted the am2 march 2022 passed A1/A2/A4/A5/C had a lot going on at the time death in family so never got back on this i have till march 24...
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Electrical Courses