Steve_P

So, in your completely unbiased yet expert opinions, this melt down was caused by what? All screws tight, earthing TT, board put in about 3 1/2 years ago, certificate unusually not only kept but with very good results.

2013-08-16 15.26.34.jpg
 
Overload on a circuit, and MCB not tripping?
The live connection onto the busbar looks loose to me!
 
They're all tight as you like mate. That melted plastic looks like grey cheese. Anyway, the bathroom is above but there's no sign of water or condensation. The only discolouring is on the left side of the busbar which looks like a white film on it. I'll be back there on Monday to have a good look over it and the heaters etc. I've got my doubts on the storage heater upstairs tbh but hey I've seen worse.


This one for starters . . .

DSCN0934.jpg
 
Busbar behind terminal. Tight now as it's welded up.
 
Had a problem with a Hager CU last week one of the lighting cables was burnt because it was not even tightened up mind you neither was the rest of the CU as I went around all the connections and made them good. Customer was not pleased as I found the fault in 5 minutes and even although I sorted the rest of the CU out he was smarting at the callout charge cheeky sod some people are never happy
 
That's true, most of them want everything for nothing. Had similar a while back where this sort of thing had happened, all the terminals were flapping about they were so loose.

I know what you're saying about it being tight now but there's something about this one that isn't right. Not sure what it is at the moment but I'll get there.

I''m even thinking about lightning, we've had a few strikes recently. BT are claiming that most of them hit earth and knocked power out up earth spikes.
 
So, in your completely unbiased yet expert opinions, this melt down was caused by what? All screws tight, earthing TT, board put in about 3 1/2 years ago, certificate unusually not only kept but with very good results.

View attachment 20311
That's not your average loose termination. There's almost no heat damage visible on the bottom of the MCB's, the busbar is still shiny across its length which means it didn't get hot enough to anneal the copper and the plastic busbar insulation didn't carbonise. The busbar distortion is also a little strange.

Do you have another photo showing the base of the CU? If you get to the bottom of what caused it I'd be interested to know, I've never come across anything similar.
 
Sorry mate, the distortion was my mate with a screwdriver poking about to see what had happened. I'll take photo's from all angles when I go back but you're right, there's something odd about this one. We've had some lightning recently, what do you reckon? I know that's a problem in some parts of SA.
 
Never seen lightning damage in a domestic CU but I'v rebuilt a couple of control panels that suffered a strike in the near vicinity. The damage was a lot more severe than your busbar above. I think lightning damage in this case is a long shot. If you can remove the 3 MCB's with the busbar still connected you can clean it up a bit more carefully than your mate with his screwdriver and maybe the cause will become evident.
 
The plastic is the weird bit. It's certainly melted but completely changed form to something that looks like gray melted cheese, the sort of stringy stuff on cheese on toast.

Aliens?
 
Aliens is also unlikely if no family members have been kidnapped. To be honest I think Tel might be right with the busbar snagged behind the clamp on the RCD but it doesn't show as much heat damage as usual.
 
There's a mad woman who lives there and would almost certainly tell us all about probing if asked.
 
Hang on, this it Cornwall, it'll be the piskies having a party in the CU at night when it goes live. One of them'll have caught their pointy little hat in the MCB.
 