Rockingit

~
Mentor
Arms
Got a new supply on a site, DNO delivered it as an SNE (so that's TN-S, yes?), 80A fuse in a 100A labelled head (yes, very clever).

But, I was there when they did it and they only ran a 'single' concentric 16mm in straight from the pole, so I can't see where the N/E separation is at all. Got a Ze of .67 so it's behaving like a TN-S.

But also, as I understand it, the DNO's aren't supposed to provide end dwellings with TN-S straight off the pole?

I'm going to be getting in a bit of a bun fight with them (DNO) over something else soon, so I'd like to be as overall gen'd up as possible!

Cheers.
 
Is there more than one pole between the house and the transformer?

The usual arrangement is earth the transformer body at it's respective pole (HV earthing). Earth the LV neutral at the next pole. This is to stop HV earth faults entering the LV system. If there’s no intermediate pole then an earth rod has to be provided at the house.

View attachment 8857
 
Last edited by a moderator:
No, it's a typical 11kV out-in-the-sticks overhead circuit, this supply is straight from a pole transformer mid-run, via the buried concentric. So, if I'm understanding you correctly, I have to provide earth rods ala TT even though they have given me an earth connection, but work with impedance figures for TNS? How the heck do I record that on an EIC and does the whole of the rest of the install have to comply with TT rules? It's stuffed if it does! Also, where is any of this in BGB??? Cheers Tony, much appreciative of your expertise in this area!
 
To be honest I don’t think they should have provided the earth, especially as they used concentric. You need to talk to the DNO regarding the HV / LV earthing discrimination. I’ll have a look later to see if I can find more info for you. (Got to go out for a while).

SWE has a lot of information but it takes some wading through even when you think you know what you’re looking for. You’ve got me hooked with this one so will put some research in to it.
 
I should have added the earth rod should be the DNO’s responsibility.

You are not responsible for the secondary transformer earthing.
 
Last edited by a moderator:
The pole/transformer are earthed, certainly. You can touch the cable inside the torn insulation down the side of the pole........
 
That will be the transformer earthing, it should be separate to the LV earthing. All sorts of problems can arise if they are combined. Under a HV/earth fault condition in the transformer the voltage gradient between the neutral and earth can reach fatal levels.

The child like drawing should explain it.

View attachment 8862

A shows where the “earthed” neutral is at a potential equal to the general body of earth if bonded at the MET.
B shows where the “earthed” neutral is at a potential above the general body of earth if bonded at the transformer.

RED being the fault paths.
 
So, just to make sure I've got this clear in my head (and it looks like there's fog on the horizon down south..);

1) Without the separate earth rod at the intake position (presumeably also clamped to the 'conventional' MET at the head), under fault conditions there may be a failure to disconnect under ADS due to lack of sufficient pd to the earth. AND,
2) under a HV fault condition, dangerous conditions may present themselves on the LV side

I thought I was being a bit of an old woman asking about something that didn't matter, but am very glad I did now!!

If 1 & 2 are true, then how on earth (lol - no pun) did the DNO not flag this up at the install? I've always found the Western Power lads fairly switched on up until now.

Mind you, what comes next in this sorry saga is a fight over a 12kw ground source heat pump, so at this rate I can see me ripping the whole lot out and building a generator house!!!!!

ps - love the artwork, nearly as saleable as mine!
 
Keep in mind it’s the DNO’s responsibility to earth the neutral. There’ll be even more fun and games if you start banging your own in!

They could have spliced an earth rod in part way on the cable run but wouldn’t have thought so. All you can do is ask them.

Best of luck, it’s looking like you’ll need it!
 
Last edited by a moderator:
Good thinking, a shot of the LV terminals on the transformer would be great.

We had a thread like this just after I joined EF, that developed in to hunt the neutral/earth.
 
RIGHT! Call off the fire brigade..... eventually after a huge amount of persuasion and not saying no, got to talk to one of the WP regional engineers this morning. Transpires that it was actually a split concentric, so it actually IS a true 3 cable TN-S supply. He did say that there is something slightly odd with that o/h circuit and transformer arrangement (something about how it used to be a standard 3ph but has been converted into 1 + 1, and there's an earth being carried on the other....sounded very waffly and I mostly switched off!) but that they knew all about it and were happy.

I've still got a call booked for a planner to attend site anyway due to loading issues (AFTER diversity, and even with a pinch of fairy-dust hope and fingers crossed my calcs are running at 140A, almost half of which are on continuous duty - on an 80A head [mis-labelled as 100A]).

The jugglers are Friday, trapeze act is Monday and the Clowns arrived weeks ago.

Many thanks though mate for taking the time - am just about to post some pics of the place on a new thread, might make you giggle when you see what I'm up against!
 
If you’re happy with the explanation then so be it.

But sorry, I’m not! There again it’s your job so it’s up to you.


There has to be a separation between the HV/LV earthing systems with an overhead supply. Where is that separation? Even with split concentric the earth point is still as in Fig B of the drawing.


A photo of the LV side of the transformer and the cut-out may put my mind at rest.


I said this one had got me interested! You can tell me to f**k off if you like but I’m not one to walk away and ignore what I think is a dangerous situation. A common HV/LV earth on a O/H supply is dangerous.


I was hoping some of the others would step in with more info on this subject.

 
Last edited by a moderator:
LOL - one of those moments, eh?! I get them myself all the time! I'm back there tomorrow so I'll take the proper camera to try to do justice to some zooming for you! Am more than happy to indulge you, it's quid pro quo on here!
 