Ring circuit. 1 leg in each 16a breaker
 

Attachments

  • image.jpg
    image.jpg
    199.5 KB · Views: 359
Can't be a ring if the ends are in different MCB /RCBO.

Doesn't mean they aren't joined in the middle somewhere tho.

Not acceptable if they are joined.
 
^As above^

You sure it’s a ring? One or other of the RCBO’s would be constantly be tripping the moment any load was applied.
 
If they're being fed from RCBO's I'm amazed (to the point of skepticism) that they are holding as the neutral current is going to be all over the shop, surely.

Therefore....how well have you tested this? It's more likely it USED to be a ring which has been split to repair it.

- - - Updated - - -

Tony - you got less to say and faster fingers than me!
 
ok my guess is that it was two radials then someone added a spur thought they needed a ring so connected up to another closer socket but it was on the other spur
 
Think you need it looked at if you say its a ring as both you RCBO's must be faulted & you have no RCD protection ! Just out of interest how did you test it to say it is a ring ?
 
IT CANNOT BE A RING AT THE MOMENT in any configuration if it's being fed from two RCBO's - it just wouldn't energise without tripping. Well, it might energise but you'd never get it to hold a load.
 
Is it not possible that RCBOs might hold? If current between respective live & neutral is in some way equal or less than tripping level it might be possible for it to hold.
 
If there was zero load on the circuit the two RCBO's would hold, but as soon as even the smallest thing is plugged in they'd trip.
 