thanks biff55 so what do you do if they don't add up? take it as thats the way it is?

exactly right , readings never tally up the same as when you work them out on paper - lots of variables temp , moisture , age of cable etc , etc.
 
what ithought, other wise you wouldn't need to take any measurements just put in what it should be.
sorry for asking question again, was getting a bit impatiant that no response then found your response.
 
Sorry just had to get things done.
Biff is right you do record the measurements you get, because that is what is there.
However in doing the three step test you should get results similar to those expected by the calculations. (According to GN3 the values should be within 0.05 ohms of the calculated result)
If I get widely varying results on the figure 8 then there is often a problem (when testing with a socket tester) with a sticky switch or dirty contacts, try switching the socket off and on a few times and inserting and removing the tester a few times and you may find your results clear up.
Based on the end to ends (which are often odd) I normally find the R1+R2 do come out about right, except for spurs.
Your results are not too far out so I do not think there is a problem, but worth checking again if you find they are very different.
 