Bit of a report on the things that stand out for me, this is just feedback and does not cover anything that looks right so does seem a bit negative overall, sorry.
Overall Try not to leave blank spaces, put N/A or some such where there is no value or it is inapplicable.
First page
You state you are inspecting and testing to the 2008 regulations but at this date you should be testing to the 2011 amendment.
You have left blank the BSEN number and rated current for the supply protective device, if it is not know then put “not verifiable” or “not known“ or “UTV”.
For the alternative source of supply this should be N/A.
BS number and type of the main switch is missing
Main switch RCD details should all be N/A
Inspections:
From the N/A items
There is no equipment present that may be affected by heat: fires, heaters, cooker switches?
There is no bathroom or other special installation in the house that needs compliance?
There is no shaver socket.
Test results
There are no electronics connected that may be damaged by IR testing, no RCDs, digital displays, transformers, fluorescent lights.
Your r2 results do not seem to match up for a 2.5 / 1.5 T+E and nor do your R1+R2 match with the calculated values.
From the point of view of space on the form you may find it easier to have >999 rather than >1000 for the IR results
G4 and G6 are very low resistances for a 1.5 lighting circuit but they could be short runs.
I put compliant in the remarks if I have nothing else to say but none would also be valid.
Rest of the form looks OK and within the readings I may expect (except the IR but not worrying levels).