the pict

~
Mentor
Is there a eol meant to be used on these I cannot get a daiagram from the net at all just sales stuff, the presen tset up has two zones one sonder on one zone and two on tother, second sounder has been disconnected but still shows a fault on sounder two, I have ahd them off but there is no indication as to what eol if any should be used
Cheers
Pict
 
what system is this on? fire, intruder? and what panel is it, make/model?
 
It is a MAG 2 fire control panel 2 zone, however the sensor heads, call points and sounders are a dolly mixture, I have manged to resovle all issues except this one on Zone 2 sounder this zone has two sounders on one circuit, the "second sounder has been disconnected for some reason but does work when tested
Pict
 
the eol is fitted to the last sounder on the line. generally it's a resistor. have a look at the other eol device. a pic would help.

tech help: esp fire : 0121 786 1881
 
Last edited:
i think the eol for sounders on this panel is a 10k resistor. check with their tech. helpline.
 