Do taps, wastes, and towel rails supplied by plasic pipes need to be bonded if protected by a 30mA RCD in the 17th?

What is protected by the 30mA rcd ?........If you mean All the circuits within the Special location{Bathroom etc], then supplementary bonding may be omitted providing disconnection times are met...main bonding is in place and the pipework is in reliable contact to the M.E.T.




spark1
 
Can someone confirm if you also have to measure the resistance from the cpc of every final circuit within the special location down to extraneous conductive parts etc, with your meter set on the low ohm range. Reading to be <1667 ohm`s in order to omit supplementary bonding.
 
Havn't got ol' red to hand but found this.

In a building with a Protective Equipotential Bonding system in accordance with 411.3.1.2, supplementary EB may be omitted where all of the following conditions are met:

1. All final circuits of the location comply with the requirements for ADS according to 411.3.2.

2. All final circuits of the location have additional protection by means of an RCD in accordance with 701.411.3.3 (ie 30ma / 40ms at 5x)

3. All extraneous conductive parts of the location are effectively connected to the PEB according to 411.3.1.2.

Note: The effectiveness of the connection of extraneous conductive parts in the location to the main earthing terminal may be assessed, where necessary, by the application of 415.2.2.


415.2.2 (in part)

Confirm that the resistance between simultaneously accessible exposed conductive parts and extraneous conductive parts fulfills the following condition:

R is less than or equal to 50 V/Ia,

where Ia is the operating current of the protective device:

for RCD's, I delta n.

for overcurrent devices, the current causing automatic operation in 5s

Should clear it all up for you.;)
 

Reply to Bathroom Bonding in the Australia area at ElectriciansForums.net

Similar Threads

Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
403
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
862

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock