Not sure I'd be happy with a combi in a steamy wet-room. The cheapy way stuff is made these days I reckon there'd be some corrosion starting after a few years. Daz.

IF it's allowed to be in there, I would be tempted to put an enclosure ( cupboard ) around it.
 
"Hello All",

This is just MY opinion about this type of situation:

Although a Boiler may be `Room Sealed` regarding the Combustion process meaning that the Products of Combustion cannot enter the Room that the appliance is located in - this does NOT mean that the Electrical components are in a `Room Sealed` position within the Boiler Casing.


Without researching individual models of Boilers to view the positions of the Electronic components - In general I would be VERY worried about STEAM getting onto the PCB and other Electronic / Electrical components if the Boiler is located in a WET ROOM / Shower Room !

And I would not be swayed in this opinion by the presence of Extract Ventilation - We must remember that Steam within a Room / Area behaves like the Vapour that it is in terms of possibly permeating into areas such as a Boiler lower casing / `Drawer`.


I hope that this is helpful to DPG / other Members / Readers.


Regards,

Chris
 
Last edited:
Aslong as your supply is ok.. Not your problem.. Y concern yourself withit?

The issue is surface tracking and polution degree. A wet room is likely to get very steamy and cause condenstaion in everything that is less than IPx6, anything that is only designed to pollution degree 2 could be subject to tracking over time.
 