sl1210

Went to look at a problem on a system boiler today that someone from British gas picked up on.

Basically the boiler is on the ground floor and was fed from a 3 pin plug plugged into a socket. The pump, timer, etc, is on the 3rd floor fed from another switched spur. When you isolate the plug top downstairs the spur upstairs is sending a voltage of 100v down the switch lines to (neutral and earth and line to earth on the supply side).
Thus making the 3 pin plug live when its unplugged.

I replaced the 3 pin plug with a hardwired switched spur and noticed that with the spur in the on position the neutral from the spur has a return path on that circuit thus making it not live. As soon as you switch the spur off and the neutral has no return path the flex becomes live again.

There is no back feed going back to the consumer unit.

Any ideas???
 
I think someone has pointed out the problem here. The pump needs a neutral at the boiler (coming straight from the pump), so somehow i need to link that up from the ground floor to the third floor
 