Chaps,

Bollard lights wired in SWA loop in/out of a henley street light cutout then flexed to the ballast. The armour is just twisted together and rammed into the cutout earth connection. I dont like this (although it's sound) and as I have to replace a length of the underground run due to damage, I would like to change the cutouts to ones that accept SWA. Are there any out there?
 
^^^^ What Lenny says!

They should be available through Neweys and other wholesalers too like.
 
them lucy ones seem similar to the ones fitted in the sense that the bottom half opens up so is there a different way of terminating the gland to normal?
 
Some of the base plates have grommets for terminating concentric cable through. The type you're looking for have brass base plates with 20 or 25mm holes in to terminate SWA glands.

Hope this helps.
 
yeah a flat base or knockouts for glands would be great. The ones currently fitted and what looks like them lucy ones, the cables are just fed through a grommet, stripped back, armour twisted and terminated. Nothing else.
 
Worked on street lighting for a few years with LA. Used the tofco units most of the time. They have a different method of terminating the cable using a fixed ferrule in the base plate and clamp the SWA of the cable to the ferrule using a jubilee clip. Similar principle to a SWA gland.
 