Hello wonderful people !!!

I have just noticed that my gas pipes have no equipotential bonding!:eek: The Gas meter is outside about a meter away from my MET. What would be the best way to bond this? Would it be to fit a clamp within 600mm at point of entry to the house and down to the MET? or what's the easiest as the gas pipe enters my house on the opposite side of the house to the MET.

How would you guys do it?

Cheers
Mark
 
the reg is it has to be bonded to the gas pipe at the meter or with 600mm of the meter but it can also be 600mm from entry to the property as long as you have accsess to the bonding piont. this all has to be conected to your main DB or met at the cut out. you say your met is next to the meter is it a TT system
 
Last edited:
If the gas meter is so close to the MET then why not run out to the gas meter cabinet and install your earth connection in there. Surface run if unobtrusive or bury it if suitable, just make sure it is at the correct depth and protected from damage.
 
Thanks Stretchyboy

That's where I'm getting confused. I thought you could install it to the meter if the meter was inside the house! If the meter was external then 600mm at point of entry to the house!
Can I actually go through the wall and outside to the meter???
 
Of course you can, the gas board actually recommend it for external gas meter housings as their guys can see that it is done without having to enter the property. We've all had our favourite customer ring us up and say" the gas man said it didn't appear to be done" or they've sent a letter saying if have to get it done etc.......
 

Reply to Bonding in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock