B
Buzz-light-bulb
Hi all
This may be considered very basic and I know the reason for bonding water and gas services is to bring all pipe work to the same potential, my question is In order for current to flow you need a different potential, so if an appliance casing has become live 230v and pipe work 0v current would flow.
Hi all
The appliance casing should be connected to the earthing system....to which the services are bonded.Therefore if appliance case is at 230v so will be the services.The difference between 230v and 230v is 0v.
If the appliance case is not connected to the earthing system and at 230v then there is a serious shock risk to anyone in contact with it and a bonded service at 0v
just to elaborate on above. the appliance case and the services will be at 230V for the duration of the fault, untill the OCPD breaks the supply to the circuit.
Surely, the appliance case and services will be at some potential between supply and earth; the value being dependent on the relative impedances of the 'line' and 'earth' parts of the earth fault loop?
Edit: and the impedance of the fault itself.
In the absense of the O.P,
I think Buzz means if the appliance casing becomes live at 230v because the casing is not earthed or the appliance earth is missing, then yes there will be 230v between the casing and the pipe which is bonded at 0v and a shock will occour to whoever touches the 2.
Hi all
That wasn't a question, it was a statement.