Evening all!
Have had a strange problem today my gut is telling me its a brown out! , We are currently working in a old cottage concealing the wiring recently rewired in surface trunking circuit at a time. Around 1500hrs We noticed the lead light (2d) would not start and quickly established a power fault. On investigation I found that as the loading on the system increased the voltage dropped considerably, under no load I was getting around 239v but with around 180watts of incandescent lighting this dropped to 217v turn as 2kw heater on and game over! Everything is rcd with no nuisance trips, all but one circuit is above 50 Mohm with the other at 2.4 Mohm so no problem there! have tried all circuits independently the only common denominator is load. Having never experienced this with a mains system I feel a little stumped. the cottage is remote and at the end of line from the nearest transformer, any thoughts?

Many thanks!
 
had this a while back...
complaint of the lighting working OK...

but as soon as the oven went on...well, it all went off...

traced it to a dodgy termination in the service head....
 
If it happens again you need to test the voltage at the head to establish whether it's an internal wiring issue or an external DNO problem. It might be worth putting the installation under some load and see if you can replicate the problem for testing purposes, put the stove, oven immersion heater and any other heaters on and check the voltage difference between the incoming supply and the ends of the circuits.
 
Checked all terms on my side, it is over head so maybe the weather has had something to do with it. Just phoned the customer and they are now able to use more power just not full yet!

- - - Updated - - -

hence why I am there! old owner had rewire on cheap!!
 
If it happens again you need to test the voltage at the head to establish whether it's an internal wiring issue or an external DNO problem. It might be worth putting the installation under some load and see if you can replicate the problem for testing purposes, put the stove, oven immersion heater and any other heaters on and check the voltage difference between the incoming supply and the ends of the circuits.
come on marvo..
i expected more from you...
i thought this would be obvious...
 
And Marvo thats what i did!

But you say the customer still has a problem this evening.....so you didn't localise the fault or establish if it's a DNO issue. I'm sure you could have found this fault if it was persistent and if you also were persistant

As Glenn says there's a very good chance it's a poor termination or incorrectly fitted busbar that's behind a clamp on an MCB rather than inside the clamp.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

SX2

-
Joined
Location
Cornwall
Website
http://www.sx2electricalsolutions.com

Thread Information

Title
Brownout? or am i missing something?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
SX2,
Last reply from
ruston,
Replies
22
Views
2,166

Advert

Back
Top