Hi, I’m currently in my 3rd adult apprenticeship and wanted some clarity on a recent fault I encountered. My friend asked me to look at his electric shower that wasn’t working. I found the fuse wire had blown.
It is a 8.5kW shower ran in 6mm. Length of cable run of about 12-15metres with 2metres of this ran in surface trunking. It has been installed for at least 15-20 years. What I wanted to know was how come it worked for so long on a 30amp BS3036 and on 6mmT&E (8500/230 =36.9A) Is this down to tolerances of the BS3036?
I have highly recommended he gets his fuse board upgraded straight away and has this booked in for end of Jan.
It is a 8.5kW shower ran in 6mm. Length of cable run of about 12-15metres with 2metres of this ran in surface trunking. It has been installed for at least 15-20 years. What I wanted to know was how come it worked for so long on a 30amp BS3036 and on 6mmT&E (8500/230 =36.9A) Is this down to tolerances of the BS3036?