Hi, I’m currently in my 3rd adult apprenticeship and wanted some clarity on a recent fault I encountered. My friend asked me to look at his electric shower that wasn’t working. I found the fuse wire had blown.

It is a 8.5kW shower ran in 6mm. Length of cable run of about 12-15metres with 2metres of this ran in surface trunking. It has been installed for at least 15-20 years. What I wanted to know was how come it worked for so long on a 30amp BS3036 and on 6mmT&E (8500/230 =36.9A) Is this down to tolerances of the BS3036?

I have highly recommended he gets his fuse board upgraded straight away and has this booked in for end of Jan.
 
I would guess it was originally a 7 KW shower when first installed,no (RCD) Residual Current Device either I guess?
The actually current depends on what voltage the power rating is tested at and what the actual voltage at the shower is.
You can look on time / current curves to see how long the fuse will last
 
A correction factor of 0.725 is applied to BS3036 fuses for cable calculations therefore this puts a 30A fuse at 41.38A which is what you base your design on, not 30A. Knowing this you can understand why it maintained the shower for so long, as to why it decided to rupture now needs looking into there could be a fault with the circuit or shower.
 
A correction factor of 0.725 is applied to BS3036 fuses for cable calculations therefore this puts a 30A fuse at 41.38A which is what you base your design on, not 30A. Knowing this you can understand why it maintained the shower for so long, as to why it decided to rupture now needs looking into there could be a fault with the circuit or shower.
Thanks that’s helps explains it. I remember 0.725 for doing cable calculations. Possible shower breakdown. He is getting bathroom/shower replaced on Monday.
 
Thanks that’s helps explains it. I remember 0.725 for doing cable calculations. Possible shower breakdown. He is getting bathroom/shower replaced on Monday.
One of the advantages of fuse wire is that you can see what sort of fault happened.A totally blasted fuse is a short circuit where as a fuse wire thats still present but has a break in the wire is overload.
My guess is that over the 20 years of the shower running it's stressed the fuse wire until eventually it breaks.
Still needs the board upgrading to RCBO's.
 
The factory my daughter works at had lost a phase, and they asked me to investigate.

Through a number of different tenants in the building, changes of use and equipment… it’s turned out that the majority of the heating (which was simply plug in rads and a few IR heat lamps) the entire office and staff room (microwave, toaster, kettle, gf grill) plus their actual machines needed for production were all off that one phase- L2. There must have been 130A at times on a 100A cartridge fuse.
That 0.725 factor has been stretched for years. (Will check if that’s different for BS88)

Everything came through a TP+N switch fuse, which the inside was particularly warm and crispy. That middle fuse holder would not budge.
Suppliers fuse, I guess would be heading the same way.


I’ve swapped over as many circuits as I can to at least let them continue functioning, shared between L1 and L3. Staff room is now separate from warehouse heating… and only half of that is on now.

None of my wholesalers just sell a fuse carrier any more off the shelf… so it would be hundreds for a brand new TPN switch fuse, or wait a few days for just a new carrier.


This is the same place that’s asking me about air-con with heating so this incident just proves what they have is inefficient as well as uneconomical.
 
The only time I have ever come across a fire, was due to a 8.5Kw shower being added to a BS3036 fuse box.
I would always insist the fuse box was upgraded due to this reason.
I don't feel something that was designed in the 1950's (guess) is up to dealing with more modern, high powered appliances.
It's not worth the risk.
I actually like the old fuse boxes. Well made and a lovely wooden box, but unfortunately (generally) not suitable for today.
 
The only time I have ever come across a fire, was due to a 8.5Kw shower being added to a BS3036 fuse box.
I would always insist the fuse box was upgraded due to this reason.
I don't feel something that was designed in the 1950's (guess) is up to dealing with more modern, high powered appliances.
It's not worth the risk.
I actually like the old fuse boxes. Well made and a lovely wooden box, but unfortunately (generally) not suitable for today.
If the cable was sized correctly and connections were all good, then I can't see how a change of fuse would have prevented a fire.
 