I have another question....

Although this is a colleague of mine who is also doing this course. He wants to use trunking, he has a lighting circuit that he can put on a 6A MCB, but when doing the correction factors calculation, the only one that has any relevance to him is the grouping factor.

So he would do In / Cg

Looking in the regs, his Cg is 0.03 as he has 30 circuits in this trunking.

6 / 0.03 = 200A
10 / 0.03 =333A

Is this correct?

Is his only option to use a separate run of trunking and split up the circuits?

Grouping factors in the regs only go up to 20 circuits. But extrapolating to a horrendous 30 circuits would only give you a grouping factor of about 0.3 not 0.03 which would require you to use a cable having CCC of 20A so you would be looking at 2.5mm2 and some large trunking.

It's also worth keeping in mind that circuits carrying less than 30% of their grouped current-carrying-capacity can be ignored when calculating the rating factor for the rest of the group. (Note 9 under table 6C in the red OSG)
 