Dont confuse things here...
metal capping is not classed as containtment, is not in the same category as conduit or trunking and is not classed as 'mechanical protection'. its sole purpose is to protect the already mechanically protected cables from the plasterers trowel.( its optional but good practice ) For this reason its not specifically mentioned in the regs.
capping does not need to be earther because the cabels beneath are T/E. ( insulated and mechanically protected ) trunking and conduit must be earthed because there ARE the mechanical protection with single core cables inside.
Ref. the avoiding the RCD usage? only SWA / SY / etc. Steel conduit / trunking ( all earthed ) can be used in that respect.
The truth appologises for foul language used earlier
and gooooood luck trying to earth 100 lengths of steel capping with 4mm G/Y cable?!
metal capping is not classed as containtment, is not in the same category as conduit or trunking and is not classed as 'mechanical protection'. its sole purpose is to protect the already mechanically protected cables from the plasterers trowel.( its optional but good practice ) For this reason its not specifically mentioned in the regs.
capping does not need to be earther because the cabels beneath are T/E. ( insulated and mechanically protected ) trunking and conduit must be earthed because there ARE the mechanical protection with single core cables inside.
Ref. the avoiding the RCD usage? only SWA / SY / etc. Steel conduit / trunking ( all earthed ) can be used in that respect.
The truth appologises for foul language used earlier

and gooooood luck trying to earth 100 lengths of steel capping with 4mm G/Y cable?!