[FONT=&amp]I’m hoping somebody can clear up a little query I have regarding cable segregation. I’ve noticed the guys on the commercial site that I am working at, are running 8723/LSF two pair screened data cable (for BMS) in the same basket & conduit as the YY/LSF mains (230v) power and lighting cables. [/FONT]

[FONT=&amp]Now I thought that you had to have a minimum distance of 50mm between u[/FONT][FONT=&amp]nscreened power cables and[/FONT][FONT=&amp]screened data cable (200mm if neither cables are screened), but they are saying that because both cables are mains rated, they can be run together?[/FONT]

[FONT=&amp]I’ve also noticed that they are cutting out the screening, I did mention that it would be best to earth the screen due to the close proximity of the unscreened mains cables and the effects of induced EMF. I know the effects of EMF can be cancelled by the twisted pair, but surely one end of the screed would need to be earthed?[/FONT]

[FONT=&amp]I haven’t got a regs book on me, but if somebody could point me to a regulation number or publication, it would be much appreciated. [/FONT]:confused5:
 
.........[FONT=&amp]Now I thought that you had to have a minimum distance of 50mm between u[/FONT][FONT=&amp]nscreened power cables and[/FONT][FONT=&amp]screened data cable (200mm if neither cables are screened), but they are saying that because both cables are mains rated, they can be run together?[/FONT]

You've stated 'segregation' in the thread title but what you're describing is 'separation'. Sorry, can't help the the regulation references but they're two different things.
 
[FONT=&amp]I’m hoping somebody can clear up a little query I have regarding cable segregation. I’ve noticed the guys on the commercial site that I am working at, are running 8723/LSF two pair screened data cable (for BMS) in the same basket & conduit as the YY/LSF mains (230v) power and lighting cables. [/FONT]

[FONT=&amp]Now I thought that you had to have a minimum distance of 50mm between u[/FONT][FONT=&amp]nscreened power cables and[/FONT][FONT=&amp]screened data cable (200mm if neither cables are screened), but they are saying that because both cables are mains rated, they can be run together?[/FONT]

[FONT=&amp]I’ve also noticed that they are cutting out the screening, I did mention that it would be best to earth the screen due to the close proximity of the unscreened mains cables and the effects of induced EMF. I know the effects of EMF can be cancelled by the twisted pair, but surely one end of the screed would need to be earthed?[/FONT]

[FONT=&amp]I haven’t got a regs book on me, but if somebody could point me to a regulation number or publication, it would be much appreciated. [/FONT]:confused5:

big. they also use yy cable to carry 12/24v for doors etc.

the cable is rated for 300v but they dont usually use it for that.

it depends on the equipement as well, i know with most of the schneider gear we use there is no were for the screen on field end for most and not always for panel end

(normally the 2c cable we use is beldon 8760 which i think is different to the one your talking about
 
Section 528.1 covers the requirements for separation of different band cables from an electrical point of view.
From a data point of view it is normally incident magnetic fields affecting the data stream that are discussed, though I believe in reality it does not often cause problems. BUT when it does it does!
 
I’m hoping somebody can clear up a little query I have regarding cable segregation. I’ve noticed the guys on the commercial site that I am working at, are running 8723/LSF two pair screened data cable (for BMS) in the same basket & conduit as the YY/LSF mains (230v) power and lighting cables. Now I thought that you had to have a minimum distance of 50mm between unscreened power cables andscreened data cable (200mm if neither cables are screened), but they are saying that because both cables are mains rated, they can be run together?

I’ve also noticed that they are cutting out the screening, I did mention that it would be best to earth the screen due to the close proximity of the unscreened mains cables and the effects of induced EMF. I know the effects of EMF can be cancelled by the twisted pair, but surely one end of the screed would need to be earthed?

I haven’t got a regs book on me, but if somebody could point me to a regulation number or publication, it would be much appreciated. :confused5:

It's one thing running these two cable systems (BMS signal/data cables and general LTG/PWR 240V cabling) on the same tray or basketwork, where they are not physically touching each other, but it's another thing altogether, running them in the same conduit. No way would i ever allow that installation to stay in place!!
 