werner starbuck

Can anybody help me please? I am trying to make semse of all the tables for cable selections and VD's. Doing the Maths is the easy part, because you use the formulae and go from there, but finding the right information from the tables proves to be my struggle. Am I making too much of it or is it really that difficult?
 
it's not that difficult. start with the design load, say for arguments sake, it's 24A. so 1st idea would be 2.5mm. at a ccc of 27A clipped direct. then apply reference method/ ambient temp/grouping derating factors, if any, and if that takes you below 24A, you have to go up in cable size. say you need 6mm to handle the 24A. then do the volt drop calc. for 6mm at 24A at whatever the length of the cable run is. you are allowed 5% on all but lighting which is only 3%. if that works out OK, you then have the correct cable size.
 
For cable types you use regularly, I find it helps to write the common name of the cable against the relevant table in the regs.
ie,
4D1A: PVC singles
4D4A: PVC insulated SWA
4D5: T&E
4E4A: XLPE SWA

Helps to avoid looking at the wrong table.
 
I am studying a DEI course. I have this question and the htables are giving me a headache. Can anybody help me please?

Question.
A d.c. circuit has a design current of 40A. It is to be wired in a two-core cable to BS7919 having 90C thermoplastic and copper conductors. It is also to be installed in trunking with five other similar circuits. If the ambient temp. is 35C and the circuit is to be protected by a 45A BS1361 fuse, what is the minimum csa of cable that can be used.

My answer so far:
Ib=40A
In=45A
Ca=0.96 (4B1)
Cg=0.57 (4C1)
It=45/(0.96 x 0.57)=82.2A
Iz=82.2A (not sure about this).
Cs=25mm 2

I'm not sure if this is right. Can anybody please guide me in the rigth direction?
 
I am studying a DEI course. I have this question and the htables are giving me a headache. Can anybody help me please?


Question.
A d.c. circuit has a design current of 40A. It is to be wired in a two-core cable to BS7919 having 90C thermoplastic and copper conductors. It is also to be installed in trunking with five other similar circuits. If the ambient temp. is 35C and the circuit is to be protected by a 45A BS1361 fuse, what is the minimum csa of cable that can be used.


My answer so far:
Ib=40A
In=45A
Ca=0.96 (4B1)
Cg=0.57 (4C1)
It=45/(0.96 x 0.57)=82.2A
Iz=82.2A (not sure about this).
Cs=25mm 2


I'm not sure if this is right. Can anybody please guide me in the rigth direction?
Hi the question is slightly odd in that 90oC is for thermosetting not thermoplastic cables and BS7919 is normally rubber cable but assuming the requirement is for thermosetting plastic cables at 90oC rating then you have your factors correct and the value of It. You do not need to know Iz.


If It is 82.2 A then you need to select from the tables a cable installed to reference method B that can carry 82.2A equivalent continuously, this is (according to the BRB not BGB) for a 2 core cable, 16mm2 in table 4E2A since this can carry 91A and is therefore the lowest csa available.
 