hightower
Awesome advice fellas, something else learned today
I'd go with 1mm too. In reality we all know this is going to be more than adequate in this instance.
Makes me laugh when I still see people wiring domestic lighting circuits in 1.5mm and then fitting about 20x 7 watt downlights on it.
even the rule of thumb of 100watts per fitting (pendants btw) would mean 1mm would be enough in a lot of casesI thought the cable size wasn't permitted to be smaller than the protective device at any point in the circuit though?
I think it would have been subject to 0.38 factor due to grouping with other circuits, and I haven't got book to hand but think that brings 1mm under 6a ccc - which people have said would be fine for a switch drop, but not if it was feeding the rest of the lighting circuit.even the rule of thumb of 100watts per fitting (pendants btw) would mean 1mm would be enough in a lot of cases
Something else learned [emoji106]Grouping factors in the regs are only applicable when the cables are operating at their full capacity 24/7. For cables loaded below 30% of their capacity for the majority of time you don't count them in grouping factors.
In a domestic install you'll never realistically need grouping