we make calculations based on a supply voltage of 230V, but in most installations the average is 245V.

now a fixed load of 6 ohms would have the following current increases
230/6 = 38.3A
240/6 = 41.0A
250/6 = 41.6A

my question is why do we use 230V when an average supply voltage is giving higher circuit currents that that calculated for been on the beer for a while now so i'm sure I have missed the point some where so my apoligies in advance
 
its the other way around --hic---
Not sure what you mean by 'the other way round'.

blue eyes is correct except the maths is not too good - 240/6 = 40.

230V (nominal voltage) is just a number used for design calculations to ensure everything complies with the regulations.
 
for example
a resistance or 8.52 ohms at 230V wil have a current of 27A flowing.assuming a 2.5mm multicore 70 Deg cable 4D2A ref b says 27A is fine (I am not looking at ccc as this is just to show my point.
the same resister fed on a 240V supply would pull 28.16A now the cable is not adiquite.
am I right?

- - - Updated - - -

sorry ref c
 
Not sure what you mean by 'the other way round'.

blue eyes is correct except the maths is not too good - 240/6 = 40.

230V (nominal voltage) is just a number used for design calculations to ensure everything complies with the regulations.
type error
 
for example
a resistance or 8.52 ohms at 230V wil have a current of 27A flowing.assuming a 2.5mm multicore 70 Deg cable 4D2A ref b says 27A is fine (I am not looking at ccc as this is just to show my point.
the same resister fed on a 240V supply would pull 28.16A now the cable is not adiquite.
am I right?

- - - Updated - - -

sorry ref c
the higher the potential difference...the more current can flow yes....
 