Sort of.
Though are you sure it's 110v there - may be 220v
The real issue may be the wiring of the transformer, often the 240v side has a fuse or overload, whilst the 55-0-55 v side may have split windings, one fused at say 32A for the 32A outlet, and the other at 16A for the 16A outlet, - in this case using it in reverse may limit the capacity as you aren't using all the windings, or limited by the size of fuse. (Smaller transformers have the single secondary, but may still have fuse size issues).
In using the transformer though you would have to re-wire it, a socket outlet on the 240v side, and socket inlets for the 110V side, it would be dangerous to use the plug/sockets the wrong way round - exposed pins must never be live.
In addition you will have to re-arrange the earths (the 0 in the 55-0-55 must not be earthed, and the neutral side of the outlet should be earthed) and it must have a proper rcd on the 240v side after the split of neutral and cpc.
So technically a transformer may be used either way round, but there are practical safety issues in configuring a 240v supply correctly.