LlandrilloSpark

Doing a PIR this morning, TNS, 16mm clamped to supply cable which leads to the MET, <100v between L&E so couldnt get Ze, there is a 6mm Earth running from the MET to the 3036 board, despite the non existent Ze if i test between the MET and line I get 240v and 0.23ohms!, there is no bonding at all, loop between L & N is 0.10ohms

Ive already phoned this one in
 
so the only earths going into the MET are the 6mm to the 3036 and the 16mm from the TNS supply?
 
I had a similar problem a while ago when doing an electric gate install; turns out the earths in the CU (particularly one that came from an SWA that was glanded into a metal JB on a metal post) were giving enough of an earth to do a Zs on the circuits but there was no Ze available. The metal post was acting as a gigantic earth rod. However in your case a 0.23 reading for a TT would be particularly good... good luck!
 
had simmilar before on a poor main earth which somehow limits the tester to >100v so test cant continue (megger) ran new earth from outside box and it cleared.
 
similar thing happening here jase, getting good Zs on all 6 circuits in the house, but cant figure it out
 
Can you not do your Ze directly from the clamp on the TN-S supply, then if you can get a decent reading you'll then know, as Ezzzekiel has already intimated, you've got a dodgy main earthing conductor.
 
Not phoned in yet as the house is unoccupied so ive placed a Napit dangerous situation notice on it and will phone it in once ive spoken to the client
last one took 6 hours to sort.
 
Its not uncommon for the dno's cable to have a poor earth hence why the main bonds are disconnected for the Ze test, many don't and it goes un-noticed. Well done for spotting it. You did not say how old the installation was but the main earthing used to be off the waterpipe years ago, sometimes just off a socket to the pipe under the floor and backfeeding the other circuits, which sounds like what you have. Did you check if it was not just a loose clamp on sheath ?
 
Its not uncommon for the dno's cable to have a poor earth hence why the main bonds are disconnected for the Ze test, many don't and it goes un-noticed. Well done for spotting it. You did not say how old the installation was but the main earthing used to be off the waterpipe years ago, sometimes just off a socket to the pipe under the floor and backfeeding the other circuits, which sounds like what you have. Did you check if it was not just a loose clamp on sheath ?

I've never disconnected the main protective bonding, just removed the earthing conductor and tested down that, as per GN3.
 
I thought the clamp was dubious to be honest, for an older installation 16mm earth is large, I usually find 6mm in these parts, so I clamped the exposed metalwork of the cable and got nothing I can only think it's rusted away underground around the circumference hence no continuity, I'll be phoning it in tomorrow I'll keep u posted
 